ajc1976
Hi all,
Hope you can give some advice:
I want to install a new bathroom in my house. This will involve a long branch pipe to the soils stack. It will be about 2.5m under a suspended timber floor (joists in the correct direction thankfully) then 4m outside to the vertical stack. The joists are 6 inches so i can get the required fall under the floor, then outside there are no probs.
My worry is the 6.5m run - building regs document H is confusing as table 2 states a 15m maximum run, but diagram 3 states a 6m max run (so I'm obviously 1/2m longer!)
Where do I stand here? And I assume tee-ing the new basin and bath wastes into this new branch is okay?
Thanks
Hope you can give some advice:
I want to install a new bathroom in my house. This will involve a long branch pipe to the soils stack. It will be about 2.5m under a suspended timber floor (joists in the correct direction thankfully) then 4m outside to the vertical stack. The joists are 6 inches so i can get the required fall under the floor, then outside there are no probs.