A boiler with suitable IP number is not an issue in zone 2, it’s a switchgear and controlgear are giving us a grief. Accessories in zone 2 must not have switches or socket outlets. A cable outlet plate is permitted.
From the 17[SUP]th[/SUP]:
Part 7 SPECIAL INSTALLATIONS OR LOCATIONS, PARTICULAR REQUIREMENTS
Section 701 LOCATIONS CONTAINING A BATH OR SHOWER
…
701.5 Selection and erection of equipment
…
701.512.3 Erection of switchgear, controlgear and accessories according to external influences
The following requirements do not apply to switches and controls which are incorporated in fixed current-using equipment suitable for use in that zone or to insulating pull cords or cord operated switches.
…
In zone2:
Switchgear, accessories incorporating switches or socket-outlets shall not be installed with exception of:
(i) Switches and socket-outlets of SELV circuits, the safety source being installed outside zones 0, 1 and 2,
(ii) Shaver supply units complying with BS EN 61558-1-5.
… sockets-outlets are prohibited within a distance of 3 m horizontally from the boundary of zone 1.
Definition:
Accessory. A device, other than current-using equipment, associated with such equipment or with the wiring of an installation.
SELV (separated extra low voltage). An extra-low voltage system which is electrically separated from Earth and from other systems in such a way that a single fault cannot give rise to the risk of electric shock.