Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Hmm flushing an old broken boiler? Prior to new combi in the Boilers area at Plumbers Forums

Status
Not open for further replies.

Jones82

Gas Engineer
Messages
221
I'm about to fit a new boiler for a customer, usually I'd add a flushing agent to the old boiler and give it a run round and hot flush but this time the old boiler is knackered and won't hold pressure.

I've thought about isolating the old boiler and manually filling via a filling loop but I'd still have no pump to circulate the agent...

Hmm would it be ok to fit a magna clean and give it a good flush with the new boiler connected?
Not ideal but I'm stumped for other options?
 
I'm about to fit a new boiler for a customer, usually I'd add a flushing agent to the old boiler and give it a run round and hot flush but this time the old boiler is knackered and won't hold pressure.

I've thought about isolating the old boiler and manually filling via a filling loop but I'd still have no pump to circulate the agent...

Hmm would it be ok to fit a magna clean and give it a good flush with the new boiler connected?
Not ideal but I'm stumped for other options?

I've recently had this problem,
Flush with old boiler a good few times,
Fit new boiler, isolate at valves
Fit a mgnaclean and flush till clean as you can get it,
Then add cleaner, hot flush should be fine with magnaclean
 
it all depends on the condition of the system, if bad then powerflush would be best, a magnaclean is designed to pic up small amounts of iron thats moving about and back to the boiler, it wont flush the system for you.
 
Status
Not open for further replies.

Similar plumbing topics

You need a new service engineer not a new...
Replies
3
Views
935
Thanks, yes I will ask him when he comes in a...
Replies
2
Views
1K
Correct way to do it!
Replies
3
Views
2K
We've just sorted one of these situations...
Replies
9
Views
1K
Thanks for this, much appreciated. Andrew
Replies
2
Views
1K
Back
Top