Terry

Central heating system with 2 off 22mm Honeywell Zone Valves, 1 for heating and 1 for hot water.

The hot water valve lasts about 6 months and then stops opening sufficiently so that the operating arm fails to hit the microswitch to switch on pump.

Have changed the head twice and valve twice, but same cycle repeats.
Fault can be cleared temporarily by removed operating head on valve and cycling valve manually.

The heating valve is installed next to the hot water valve in the same orientation and never suffers from this fault.

Any ideas please
 
if you still have the failed ones you could try honeywells maybe they could give an answer
are you sure water is running in the right direction through both valves
its rare for what you describe to happen as these are normally quite reliable pieces of kit and usually its the motor that packs up first the motor can be changed cheaper than a complete head
 

Similar plumbing topics

  • Question
The eTRVs would have to open before the zone...
Replies
14
Views
2K
  • Question
Hi I have a Honeywell ST699 programmer which...
Replies
0
Views
675
J
  • Question
the micro switches in the zone valves fail …...
Replies
3
Views
805
Murdoch
M
T
  • Question
Yes, even though strange that you have that...
Replies
9
Views
1K
  • Question
If you have test equipment then you could test...
Replies
1
Views
842
Deleted member 120897
D
Back
Top