Stormingjock

Could really do with some advice please. Just moved into a new house with polypipe underfloor heating in 3 out of 4 rooms but only 1 room is getting warm. I've taken a picture of the manifold and it's clear that there is an issue but how do I fix this?
 

Attachments

  • image.jpg
    image.jpg
    96 KB · Views: 69
Yes, that's correct. This is the only pipe that's got any hot water flowing through it. Concerned that the temp gauge is off the charts. Can I bleed the system myself or best leave it to the installer? Not come across this system before.
 
For a temporary measure you could unscrew the thermostat head which would allow heating to flow down the cold circuits when it's operating!

Looks like room thermostats not opening the valves.
 
Id make sure the blending valve is down at around 45 degrees, if the U/F gets too hot you risk damaging the flooring above it!

If the room stats are R/F which Polypipe do use then check the batteries as the power no heat!
 