Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Promax 28 boiling when hot water is used????????? in the Boilers area at Plumbers Forums

Status
Not open for further replies.
R

Richie_77

Hi all
Went to a promax yesterday and the thing doesn't seem to be modulating down on the hot water causing it to overheat and boil.
I'm guessing its the hot water thermistor that sits on the brass body in front of the plate heat ex has become dirty and needs cleaning or am i missing something????
 
Is DHW hot? Or does it go cold? Does boiler over pressurise as it's boiling it's **** off ? If so it sounds more like the plate. Easy was to tell is if temp sky rockets when initially fired in DHW.
 
There's several things that could be the issue here. Firstly, the ntc could be relaying the wrong resistance to the pcb. Easy was to tell is, get your multimeter and test the resistance. When cold it should be about 12 kohms. Usually you get a fault code of E50 when the sensor is faulty, but I have had exactly this when the primary ntc was faulty. The temp was saying 8 degrees, but rads were very hot. This would cause the overheat on both ch and dhw though.


Another fault could be the plate heat exchanger, may be blocked or scaled causing boiler to overheat.

Thirdly, the diverter valve passing will cause the boiler to continually try to get the water hot enough. When the ch is off and cold, feel the flow pipe whilst running the dhw and see if it gets hot.
 
Well as it turns out plate to plate was blocked solid and the change over valve too bathed the plate to plate in hydrochloric acid for 15 mins cleaned out the change over and done very happy customer
thanks for all your comments
 
Status
Not open for further replies.

Similar plumbing topics

Probably temperature sensor or thermistor that...
Replies
4
Views
771
The filter cartridge doesn’t have a wrapper on...
Replies
11
Views
3K
That is manifold fo4 all rooms on 1st floor...
2 3
Replies
58
Views
6K
Looks that way, a multimeter would tell alot...
Replies
8
Views
882
L
Replies
2
Views
2K
Back
Top