Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Really badly choked up boiler in the Boilers area at Plumbers Forums

Status
Not open for further replies.

Millsy 82

Plumbers Arms member
Plumber
Gas Engineer
Messages
4,350
I went to an 18 month old Grant vortex combi 26 which was the worst i've ever seen to the point that the baffles had an inch of soot on top of them and when I pulled the swirl baffles out they were solid with soot. I cleaned it all out so it was sparkly clean changed nozzle etc etc

I was expecting he oil pump to be too high pressure but it was at 8 bar and the air setting was about 5.5 which I wouldnt of thought would be too far out. but it was smoking a treat so opened the air up until it was fairly clean then put my analyser in and I cant get the co2 below 12% with the oil pressure on 8 and I had to wind the air as far as I could.

In the end I dropped the oil presssure to 6.5 bar and I managed to get the co2 down to 11.4%. What I cant work out is why with the air fully open will it not drop below 12% is it because

A Its still burning off some muck around the heat exchanger. (this is my thought)

B They are not using Kerosene? and maybe using gas oil or even red diesel or something else?

Im going back early next week to check it again as it was so hoping it burns off all the muck and I can just reset it all back up and away it goes>
 
Hmm... What colour was the oil?

red diesel is gas oil btw :)
Did you change the nozzle?

also if its new, did you check the burner had the correct blast tube?
 
Last edited:
Should have dropped a smaller nozzle in for a week to help burn it off. I wouldn't want to stick my meter in that for a week. Have you checked the analyser filter?
 
wrong nozzle been fitted, or flue seal gone causing pocs to recirc, for 2 ideas
 
Yeah gave it a full service so new nozzle hose etc.

I didnt realise gas oil and red diesel were the same lol. It looked like kereosene to me
 
Did you check it was the right nozzle in the box? Flue is probably choked too, chuck a soot breaker in :/)
 
wrong nozzle been fitted, or flue seal gone causing pocs to recirc, for 2 ideas

Checked the nozzle before I put it in to make sure it was what was written on the tub. Right nozzle for the boiler as I double checked the manual. I ran the boiler with the air hose disconnected as well no difference as I thought it may be something like that.
 
Yeah gave it a full service so new nozzle hose etc.

I didnt realise gas oil and red diesel were the same lol. It looked like kereosene to me

Did you replace the nozzle like for like or as per MI's?
i always get them up on my phone as i would say about a tenth of what i go too have the wrong nozzle!!

yup!
 
Should have dropped a smaller nozzle in for a week to help burn it off. I wouldn't want to stick my meter in that for a week. Have you checked the analyser filter?

Analyser filter was clean I made sure it wasnt smoking before I put it in and the inside of the boiler was spotless by the time I finished on it. (Me on the other hand was covered from head to foot in soot!)

Do you reckon it could just be burning of the muck still then? Ive worked on loads of oil boilers over the last couple of years some badly choked up but none this bad and never came accross this problem.
 
Smells very different also. Were the FGA readings any better with the snorkel removed?
 
CO was fine cant remember what it was and all paperwork is in the van down the road. I will get the readout out in the morning.
 
Last edited:
If the CO was good, you must have done a beautiful clean then, should have been a surgeon.
 
If the CO was good, you must have done a beautiful clean then, should have been a surgeon.

I couldnt be a surgeon I dont mind my own blood but others and I feel sick lol.

It was between 50 and 60 if I can remember right but I did leave it running for half hour before doing it. And I spent ages cleaning it as I always do so I hope it was a beautiful clean.
 
Keep the oil pressure at 8 bar, disconnect the snorkel if any doubt about it or flue, check the air damper inside the burner is actually opening when you turn the Allen bolt - many can be broken on RDBs. Be sure to tighten new nozzle up fully. (easy to forget)
Unlikely, but you can have a faulty new nozzle putting loads oil out.
Co2 will be fairly decent if you removed 99% of soot. Smoke pump will show yellow reading when setting good, until all soot is gone after a day or 2.
Maybe not in your boiler, but look out for a mouse nest inside snorkel or a dead mouse inside burner or other debris - only takes a minuscule bit of fluff in the narrowest, smallest points of the burners air intake to blast tube to reduce air by large amount.
 
Last edited:
As said check you have the right blast tube, the vortex can change how it burns.
 
Badly sooted i normally drop out a baffle or some of the spirals or springs in the condensing heat exchanger and set it lean. Then back after a week and sort it properly.
 
I also would put the air up a little to keep it on the safe side & let it clean itself out for a few days.
I still use a smoke pump just to reasure myself that it's not still running black.
 
I think you may have sorted it, just needs time to settle. It would struggle to light on diesel if at all.
 
I presume it has 1 of those Riello RDB burner on it. This is gonna sound mad but on some models you know where you adjust the air, that's not the only air adjustment. If you take the burner out, there's a couple of screws holding the plastic casing on around the air louvre side with the air intake on the right hand side. If you remove the plastic cover to see the fan impeller there's actually another adjustment louvre. I only know this cos I got caught out with that before. So check that out, some Riello Burners have this. Check it out, it's worth a shot
 
I presume it has 1 of those Riello RDB burner on it. This is gonna sound mad but on some models you know where you adjust the air, that's not the only air adjustment. If you take the burner out, there's a couple of screws holding the plastic casing on around the air louvre side with the air intake on the right hand side. If you remove the plastic cover to see the fan impeller there's actually another adjustment louvre. I only know this cos I got caught out with that before. So check that out, some Riello Burners have this. Check it out, it's worth a shot

Was thinking same, - the inner is a air adjustment which should be set, in theory, for the burners actual output.
The outer is for fine adjustment - normally all that needs adjusted hopefully.
 
I presume it has 1 of those Riello RDB burner on it. This is gonna sound mad but on some models you know where you adjust the air, that's not the only air adjustment. If you take the burner out, there's a couple of screws holding the plastic casing on around the air louvre side with the air intake on the right hand side. If you remove the plastic cover to see the fan impeller there's actually another adjustment louvre. I only know this cos I got caught out with that before. So check that out, some Riello Burners have this. Check it out, it's worth a shot

Do you mean the louved disk you set round to your outputs?
 
Status
Not open for further replies.

Similar plumbing topics

I've tidied up this thread and banned a user...
Replies
2
Views
882
    • Like
Did you ever get an answer to your problem? We...
Replies
11
Views
12K
Think the appropriate phrase for this should...
Replies
4
Views
1K
All stats have a hysteresis but I couldn't...
2 3 4 5 6
Replies
141
Views
28K
H
  • Locked
I had a dead mouse in a Rayburn combustion...
Replies
6
Views
3K
Back
Top