Hi all, after searching and not finding a wiring diagram for s plan plus I have been racking my brain as to how to wire it. Could someone please confirm if my attempt at wiring in this picture would/would not work for adding another zone on to an s plan?
On the official wiring plan from ecowarm (thanks again) the new zones stat is wired to a permanent live from the consumer unit. In mine I wired it up to the switched live from the programmers CH side. Does that mean that the zone with a permanent live can operate the CH independantly, but on my wiring the zone is getting power from the programmers switched live it will only work if the programmer is calling?
I see, so I would be in effect using the time clock from the main programmer for the zone but even better would be to wire so each zone has its own time programmer like the official one.
Last question, for a combi would you just treat it the same but with a CH only programmer and without the wiring for the pump, cylinder stat & HW zone? Like this: