Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Sterling 40 coil voltage in the Boilers area at Plumbers Forums

Status
Not open for further replies.

bennythedip

Gas Engineer
Messages
162
Hi all,
Had a quick look at a sterling 40 this evening. There was no oil going to nozzle but definitely oil in the pump. I checked the voltage going to the coil and its 80volts. Is that enough to open the valve? Didn't have magnet to stick on it to see if it would run. All your input appreciated.
 
duff solenoid, jammed valve hard to say as I just stick a solenoid tester over the top to see if it lights up or not more important is whether or not you are getting the correct pressure off the pump to push the nozzle spring open, which negates the need for voltage test really.
 
Was only a quick stop on way home, thought it might be a 5min job. Not much fun when it's pitch black with hail stones battering off ya so I just left it!
 
silly boy, only work on external boilers when the sun is shining
 
can't work on them in the wet, my risk assessor says I might get electrocuted :)
 
Just for anyone that's interested, the photocell was faulty. I rembered I came across this a few years ago as I wouldn't work on a sterling burner too often. I'm still not sure if it means that the correct voltage is not sent out when it checks resistance of photocell or not. I forgot to check what's the voltage sent out to coil when it's running correctly. It's a sneaky one!!
 
There is normally 50-80v to coil when boiler in purge mode, this is then upped to 230-240 when coil needs to be energised.
 
Status
Not open for further replies.

Similar plumbing topics

I mean you can test with a multi meter on the...
Replies
9
Views
733
  • Question
OK thanks for the response. I hadn't...
Replies
5
Views
791
Seemed so, for that first half hour. House had...
Replies
12
Views
5K
S
OK then, good luck with it 👍👍
Replies
3
Views
1K
Back
Top