sasik
My customer have a Santon unvented hot water cylinder. The cylinder will discharge water when the system heats up (it will run water constantly from the discharge pipe).
I tested the pressure in the expansion vessel and in the hot water outlet when it was discharging and the pressure was over 6.5bar in both! I then drain the system down and the pressure in the vessel was very low so I recharge it back up to 3.5bar.
I refilled the system turn the boiler on and when the system heated up it discharged again!!
I tested the pressure again in the expansion vessel after I drined the system down and this time the pressure was 3.5bar fine! I tested the pressure in the hot water outlet point and the cold outlet point and the pressure is fine (equle pressure 3.5bar).
I know the high temp' relife valve is fine and I also know the combination valve/pressure relife valve is fine (it's brand new).
So what could be the problem
Thanks Sasi
I tested the pressure in the expansion vessel and in the hot water outlet when it was discharging and the pressure was over 6.5bar in both! I then drain the system down and the pressure in the vessel was very low so I recharge it back up to 3.5bar.
I refilled the system turn the boiler on and when the system heated up it discharged again!!
I tested the pressure again in the expansion vessel after I drined the system down and this time the pressure was 3.5bar fine! I tested the pressure in the hot water outlet point and the cold outlet point and the pressure is fine (equle pressure 3.5bar).
I know the high temp' relife valve is fine and I also know the combination valve/pressure relife valve is fine (it's brand new).
So what could be the problem
Thanks Sasi