Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Worcester heatslave 18/25 (oil) combi in the Boilers area at Plumbers Forums

Status
Not open for further replies.

ShaunCorbs

Super Moderator
Staff member
S. Mod
Plumber
Gas Engineer
Subscribed
Messages
34,635
Solutions
1
right went to a call out today no hot water and a blown 3amp fuse,

just to let you know im not the first heating eng to be called out client said shes had 4 including me

worked out what it was (2 channel prog) and the link was missing in the hot water side so unless timer was on hot water 24/7 it wouldn't give hot water

sorted that anyway

fired all up good 10 mins running hot water then switch to heating etc fine, just about to go thought i better test it again so turn hot tap on and nothing bang fuse blown, put a new one in tried heating and nothing bang fuse blown,

managed to get it not blowing fuses, turn tap on nothing (boiler doesnt fire) pump runs thats it

so phone worcester up to see if i have missed anything so went through the questions overheat stat got power in and out etc, he said it should fire and if it doesnt it the control box (pic below) and also the cap is leaking

image.jpg

also this flashes (well one quick flash, one long flash about 1-2 seconds, then 5 seconds of nothing)

image.jpg

is he right (dont do oil much) or is there any funny or anything else that i have missed?

many thanks
shaun

ps any question ask away
 
Last edited:
guess not :(
 
Control box does normally have little sparks as contacts make, its normal. Capacitor will need changing but not had one blow fuses. Try and pinpoint fault by unplugging burner and see if everything else runs ok then plug back in and see if blows. Flue high limit corrodes on them but dought would blow fuse. If tripping when tap on could be flow switch.
Just a few quick thoughts.
 
The DKO control box is a self diagnostic gizmo. The sequence of flashes lets you know at what point of ignition the burner is at. If its locked out then the sequence of flashes lets you know at what stage the burner was at when it locked out.
 
Control box does normally have little sparks as contacts make, its normal. Capacitor will need changing but not had one blow fuses. Try and pinpoint fault by unplugging burner and see if everything else runs ok then plug back in and see if blows. Flue high limit corrodes on them but dought would blow fuse. If tripping when tap on could be flow switch.
Just a few quick thoughts.

thats the thing nothing runs except the central heating pump and yes the reset button flashes in above sequence
 
The DKO control box is a self diagnostic gizmo. The sequence of flashes lets you know at what point of ignition the burner is at. If its locked out then the sequence of flashes lets you know at what stage the burner was at when it locked out.

you got a list of them as nothing was in the mis
 
just found a very old book with

❘ ❚ _

Internal fuse defect
> control box defect

looks like im on the right lines
 
IIRC .. 1 short pulse , 1 long pulse followed by a long pause is a control box fault. This could be caused by the failure of the motor.
 
IIRC .. 1 short pulse , 1 long pulse followed by a long pause is a control box fault. This could be caused by the failure of the motor.

Ye something's taken the box out probably, test as much as you can before slapping new box in or you'll end up with a pile of them!
 
Status
Not open for further replies.

Similar plumbing topics

All fixed. Changing the nozzle and cleaning...
Replies
4
Views
539
W
pcb issue so gas safe engy required sorry to say