Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Working pressure low at boiler - ncs or at risk? in the Boilers area at Plumbers Forums

Status
Not open for further replies.
B

beesley121

Hi guys,

went to a goosed combi that was running on 15mm pipe work that goes an estimated 15m. Flue had not been up in properly and wasn't seal so ID'ed it. Took a wp before I told it off and it there was 4mb drop over the installation pipe work.

now if the boiler had been working ok, would this just be an ncs??

reason why is because I installed a new ideal logic 30he today. Told them that the pipe work wasn't big enough but would install boiler and see what the results were. Anyway, 21mb at meter wp, 14mb at test point under boiler.
Now obviously the pipe work needs upgrading, in the mean time though, is this situation an ncs or now at risk as I can't commission the boiler properly. Flue gas is fine
 
Ncs unless it's causing other appliances to suffer then it's AR

Thanks for the reply.

i don't get this though. If it's only an ncs, does that mean I don't have to upgrade the supply? What's the point in the 1mb drop from meter to appliance
 
You can't install something to NCS, as it's a new install it has to comply.
 
No you are upgrading it! You don't fit stuff incorrectly then it becomes ok if it's only ncs or only AR. Ncs is as bad as an ID on a new fix. It's shameful! 50 hail. Croppies and two hundred lines. I am not going to become another Cowboy.
 
I understand. It will be getting upgraded but in the meantime, am I ok to leave it on or does it have to go off?
 
You cannot fully commission it, until it complies, therefore, should not leave it on and cap it off until it does comply. Gas Safety Regs.
 
on new installation no more than 1 mb difference at meter and boiler test point under boiler. did you not work out the gas pipe size . if it was an existing install as long as you get min burner pressure its ntcs but you have upgraded the boiler so it must be correct.
 
Status
Not open for further replies.

Similar plumbing topics

I feel for you, it's a bad position to be in...
Replies
18
Views
2K
Pump/feed/expansion are piped/in wrong...
Replies
9
Views
1K
Good job buddy. Rather than a beer, if you’re...
Replies
24
Views
3K
P
  • Locked
Doesn't matter, mod will remove or close it.
Replies
3
Views
863
Normal as they only get paid 150-200 per install
Replies
11
Views
2K
Back
Top