beesley121
Hi guys,
went to a goosed combi that was running on 15mm pipe work that goes an estimated 15m. Flue had not been up in properly and wasn't seal so ID'ed it. Took a wp before I told it off and it there was 4mb drop over the installation pipe work.
now if the boiler had been working ok, would this just be an ncs??
reason why is because I installed a new ideal logic 30he today. Told them that the pipe work wasn't big enough but would install boiler and see what the results were. Anyway, 21mb at meter wp, 14mb at test point under boiler.
Now obviously the pipe work needs upgrading, in the mean time though, is this situation an ncs or now at risk as I can't commission the boiler properly. Flue gas is fine