Andymav

hi guys looking for some technical advice just replaced a drayton ZA5 actuator valve head as when the customer was putting the hot water on they were getting heating aswell the problem ive found is that the valve stays open constantly, when power is cut to the system it closes but when i switch the power back on it opens and doesnt shut so it allows hot water to flow to the heating aswell as the hot water circuit they have a vailiant ecotec boiler and a megaflow pressurised cylinder i cant figure out why the valve doesnt close off the flow to the heating


andy
 
valve.jpg
 
it cant be a wiring issue because the valve was wired the same way exactly so im assuming this vault has developed
I would bet as this is a new propery the fault is wiring and has been there all the time.
Like others have said check that grey is live with the mains on and when calling for heat the brown becomes live. Also check the brown does not become live when other valves are calling. This would indicate a back feed.
a picture inside the junction box would be helpfull
 
I would bet as this is a new propery the fault is wiring and has been there all the time.
Like others have said check that grey is live with the mains on and when calling for heat the brown becomes live. Also check the brown does not become live when other valves are calling. This would indicate a back feed.
a picture inside the junction box would be helpfull

Could be a loose wire in the jb have u asked the customer if this has just started to happen or has always happened

Is the heating system getting luke warm or hot

Is it the rads in the bathroom just getting hot
 
I would bet as this is a new propery the fault is wiring and has been there all the time.
Like others have said check that grey is live with the mains on and when calling for heat the brown becomes live. Also check the brown does not become live when other valves are calling. This would indicate a back feed.
a picture inside the junction box would be helpfull

Your must have a brilliant mind as think alike?
 
ok gonna head back there and re look at the wiring in a couple days il check the grey wire and brown wires as suggested and il take some more photos hopefully its acase of swapping some of the wires around
 

Similar plumbing topics

  • Question
I have a CH circuit on a 2 way zone valve...
Replies
0
Views
606
J
  • Question
the micro switches in the zone valves fail …...
Replies
3
Views
805
Murdoch
M
  • Question
Will be a 15-60 then prob ups2 Green lights ?
Replies
8
Views
1K
  • Question
Yep, that's it. I've uploaded a video to...
Replies
9
Views
2K
  • Question
If you have test equipment then you could test...
Replies
1
Views
842
Deleted member 120897
D
Back
Top