Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss 105HE pressure swtch problem. in the Plumbing Jobs | The Job-board area at Plumbers Forums

Status
Not open for further replies.

stings27

Gas Engineer
Messages
59
Went to a mates house yesterday who had no heat/water.
Boiler goes thro' sequence, fan starts then nothing.
Fan icon on display flashes.
Followed fault finding say's to replace PS which I have. Still nothing. :angry_smile:
But on removing the - tube from the flue assembly she fires.
Put the tube back and out she goes.?????

Anybody ?????
 
This is a issue to be solved by a GSR

If you post your location. In sure one of us will be local and able to help
 
Anybody???? No. Not anybody. A gas safe registered engineer. What you are attempting is not a d.i.y job IMHO.
 
So am I pal! Do you want my GS number?? I install and have little to do with breakdowns. Just need a little friendly advice , so screw your neck back in. IMHO
 
Ok. What's your gs number and Id card number
 
Looking at the 2 posts you have made in the last 2 years I'm confident you are not GSR.
 
Have you checked the flue seal from fan to flue?? Had one a few months ago that had rotted through, was only a steel jubilee clip type with no rubber seal in.
 
:oops:

Neck well and truly back in! Chaco the Venturi and flue ways are clear would be the first thing to check.
 
Thanks goz.
Its held together with two metal bands which both look in order.
Had the fan off, all seems ok.
Just cant understand that soon as you take the negative tube off, the thing fires up.
It's as tho there's + pressure going to the PS rather than -
 
switch them over and check, i went to a biasi yesterday that had half the screws missing case
off and it was obvious someone had been in the pcb but the guy swore blind nobody had looked at it.
 
Check your pm's
 
well reading this thread AND KNOWING THIS BOILER BACKWARDS if the aps has been replaced you have a venturie,fan or flue problem
 
Status
Not open for further replies.

Similar plumbing topics

W
pcb issue so gas safe engy required sorry to say
Replies
1
Views
700
Looks like a faulty or incorrect set Automatic...
Replies
29
Views
5K
It's part of a service for me, quick check...
Replies
5
Views
3K
    • Like
had several situations where pressure relief...
Replies
7
Views
2K
  • Locked
Hi Everyone, Thanks for all the help, went...
Replies
22
Views
466
Back
Top