S

sgw869

Hello
I live in Spain and at last we are have gas piped to our urbanization
Question is from the underground supply the installer has run 15mm copper supply pipe
The pipe work has approx 12 soldered bends and the run is approx 10-12 metres
This pipe is supposed to feed four properties
When the pipe reached the central point of the four properties it splits four ways and I can only assume that is where the meters will go.
I am contemplating a 24kw combi boiler, my question is will the 15mm supply pipe be adequate to run one boiler, let alone four in total
Also there is the gas ovens and hobs to add to the equation
I can supply photographs if this would help
Best regards
Sgw
 
it depends what preasure they supply the gas at as to the pipe size im sure there was some one on here who has worked in spain
 
Depends on the pressure. It is usually higher on the inlet to the meter and governed down to working pressure from there.
Best speaking to the guys doing the work.
 
Sounds like you need to get in the pro's, bet the gsr doesnt cover Spain lol
 
It's probably LPG and they may install regulators at he property.
 
Aint got the slightest. Never heard of it 15mm feed upstream to feed four meters and then more appliances I'm loast.
 
Aint got the slightest. Never heard of it 15mm feed upstream to feed four meters and then more appliances I'm loast.

I'll put my money on it being from a comunal lpg bulk store, supply from it medium pressure to the meters and goveners to knock it back down to low pressure.

will have to be a flipping big bulk store for the vapour take off rate to be high enough though?
 
Going back to the original post.

If I lived in Spain I would have solar thermal, with electrical back up ?

Why a combi ?

The suppliers will be supplying gas for cooking/gas fire only ?

Different regs I am sure.

Bearing in mind the country is nearly bankrupt I doubt they are forward planning too much !
 
Hola To you all
Firstly many thanks for all the replies
In Spain at last in our area the supply is going to be piped natural gas
What Tamz has posted..the supply pressure is usually higher to the meter....
Hopefully this will be sufficient and the answer i was hoping for
Combi is my choice 24kw to serve 7 Rads
The Spanish are installing the gas supply...No other choice...
I will then get English engineers to do the rest
I have posted a few photos of the 15mm gas pipe and manifold installation
I would like your views on them
Many thanks
Sgw IMG_4.jpgIMG_6.jpgIMG_9.jpg
 
What's all the damage to the popes in the first pic? Corrosion, burnt?
 
Hi
Its the residue from the soldering, the joints aren't wiped clean
Sgw
 
Status
Not open for further replies.

Similar plumbing topics

Experience tells me 10mm won't be enough but...
Replies
5
Views
846
N
Thank you all. The wording was ambiguous in...
Replies
6
Views
890
Northgan
N
A bit late but what were the test results, did...
Replies
10
Views
3K
Purely for interest, on large gas lines it...
Replies
3
Views
2K
Yeah sorry, crappy powerpoint skills rather...
Replies
4
Views
3K
Back
Top