Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss 2 rads not working in the Gaining Plumbing Experience area at Plumbers Forums

Messages
12
A 5 bed house with 20 radiators.
18 of the rads are on the original microbore system, the last 2 which are in the extension are in 15mm pipework.
The problem is that the 2 in the extension never heat up!
The client has had 2 plumbers out who have balanced the system and tried putting chemicals in the system but they still do not heat up.
I think they heat up when all other rads are switched off.
They are both suggesting a power flush at about £1300 but all the other rads work fine.
Could it be a pump undersized issue or will it need the power flush?

Any suggestions appreciated.
Thanks
Phil
 
You asked for a suggestion, you got one.

Going by what you've told us the system hasn't been balanced properly.

Post a thread in the 'I'm looking for a plumber / gas engineer' section of these forums remembering to include your location - [DLMURL="http://www.ukplumbersforums.co.uk/im-looking-plumber-gas-engineer/"]I'm looking for a Plumber or Gas Engineer[/DLMURL]
 
Is the ch system dirty?
when were the radiators installed?
has the system been power flushed before?
Were those two plumbers reputable?
what pump is installed currently?
has a new boiler been installed recently?
were the new radiators installed by plumbers?
Where does the new pipework connect to the microbore system?
Did the radiators heat up when first installed?
Where is the microbore manifold?
how far is the 15mm run to the rads?

more helpful?
 
Seems to be a reoccurring problem with microbore some (lazy/untrained) people just merrily connect 15mm to the nearest pipe and assume it will work. Probably a pipe work problem as already stated.
 

Similar plumbing topics

Thanks :) . A happy new year to you!
Replies
23
Views
1K
Replies
0
Views
448
  • Question
I can't afford it at the moment, but I had one...
Replies
2
Views
460
You seem to have got it sorted, but for future...
Replies
7
Views
945
Thanks a lot, put lots more turns on + some...
Replies
6
Views
910
Back
Top