Hi all,
Was wondering if anyone had come across this before or might know what the problem is.
Trying to adjust the air gas ratio on a 28i junior. Put it in service mode. Turn the dial to maximum. Boiler goes to full output. Adjust the valve to get the reading I need. All good. Then turn down to minimum and the boiler won't stop modulating up and down so impossible to get a reading to adjust the gas valve.
Anyone got any ideas?
Many thanks,
Nat
Was wondering if anyone had come across this before or might know what the problem is.
Trying to adjust the air gas ratio on a 28i junior. Put it in service mode. Turn the dial to maximum. Boiler goes to full output. Adjust the valve to get the reading I need. All good. Then turn down to minimum and the boiler won't stop modulating up and down so impossible to get a reading to adjust the gas valve.