Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss 3 way valve replaced and not working in the Gaining Plumbing Experience area at Plumbers Forums

S

Sime

the old 3 way valve honeywell unit replaced after a power cut central heating works no hot water so I replaced it and now still no hot water and the unit is warm too touch like the old one i replaced any ideas wondering about changing the programmer which is Towerchron 2000 help needed thanks
 
It will be either the cylinder thermostat or the programmer

Central heating only lights the boiler via the orange wire from the valve.
HW only or HW & CH lights the boiler via the cylinder stat, which is powered from HW On terminal of the timer.


If you have a multimeter:

Check for 240V at the programmer HW ON terminal, with HW ON continuously.
NO 240v = faulty programmer

If OK, check 240V at the common terminal of the cylinder stat
NO 240 V = faulty wire from programmer to cyl stat

If OK, turn cyl stat to Max and check for 240V on terminal 1 of cylc stat
NO 240v = faulty cyl stat.

If OK, check for 240V on terminal with valve orange wire connected.
NO 240V = faulty wire to cyl stat.

The boiler should still light if the lever is locked in the MAN position.

Motorized valves do get warm to the touch - it does not mean it is faulty. So you may have changed it unnecessarily.
 

Similar plumbing topics

So, (Lever on Auto) does HW work on its own...
Replies
14
Views
2K
  • Question
I should have said, number 4 in the picture is...
Replies
1
Views
600
  • Question
They need to hold there g3 certificate eg...
Replies
4
Views
441
Remember, the HW even when porogrammed off...
Replies
3
Views
820
In the end decided to follow Chuck’s advice...
Replies
11
Views
678
Back
Top