hi guys this might sound really stupid but i am fitting some radiators in an extention. the builders forgot to mention there were 4 and i only thought there were 3. they are going 2 up and 2 down. they will be on either side of the walls. now because my brain was turned off i ran 15mm pipework to feed these, trouble is im not sure if i should have used 22mm. will these rads work porperly with only 15mm pipe runs? im guessing they may take longer to heat up.

at the moment they have a vented ch system but are toying with the idea of a combi boiler.

hope you can help, thanks all.

J
 
If its only 2 rads up and down it will be ok, best practice 22mm then 15 mm tails but it will be ok.

Brian
 
thanks brian. i was sweating my nuts off thinking i had to do the runs all over again. i knew best practice was to do 22mm runs, i think my brain must have just turned off or something, ill know for next time.

cheers,
 
Status
Not open for further replies.

Similar plumbing topics

Replies
9
Views
989
  • Question
Just use a compression elbow, we wont tell.
Replies
14
Views
2K
  • Question
I’m using them at present, but you can have...
Replies
12
Views
1K
Yes i already knew that but thanks for the...
Replies
8
Views
3K
Unfortunately just because it works now...
Replies
6
Views
5K
Back
Top