HI all
ive got a unvented system in the loft at home. We had the water feed replaced and at the stopcock, we get about 2 bar, and 24l/min
Showers get about 10L/min and taps around 12l/min - both around 1.5bar. The house seems to have 22mm from the stopcock to the boiler and around the house, with 15mm feeds to the taps/showers. The showers are not a great experience currently!!
My issue is, if we go accumulator, i dont think we can find anywhere to house it near the main tap - can it go elseswhere on the system? or maybe in the shed?
And is there any other option other than accumulator?
Thanks for any advice in advance!!
Steve