Hello All
My house is 15 years old, Ideal FF370 boiler, plastic 10mm pipe, Wilo Gold 60 pump (16 radiators including several small ones). Inhibitor was put in 15 years ago. Since then, nothing. Never been drained.
The only maintenance has been replaced bearings on the boiler fan, replaced actuators on zone valves and 2 boiler services (if it ain't broke, don't fix it).
Anyway, this winter a few radiators have been slow to heat.
Yesterday morning I cleaned the F&E tank. It only had a thin layer of orange dust. No sludge. I then put in 2 litres of Sentinel X400 cleaner and I'm leaving it for a few weeks.
The pump has always been on setting 2, but yesterday afternoon I put it onto 3 and that caused the cooler rads to heat up better.
The pump isn't particularly noisy. It's probably noisier than it used to be, but if the 3 setting makes a big difference then perhaps it's getting weak.
Bearing in mind the F&E tank was fairly clean, I'm not expecting a lot of sludge in the system. Or am I wrong ? I'm cleaning and draining / flushing it anyway.
So, the pump is not noisy, but 15 years old and maybe not as muscular as it was once ... Would it be sensible to replace the pump when I drain in a few weeks ? Have I had my money's worth from this Wilo pump ?
I'm looking forward to hearing the voice of experience
My house is 15 years old, Ideal FF370 boiler, plastic 10mm pipe, Wilo Gold 60 pump (16 radiators including several small ones). Inhibitor was put in 15 years ago. Since then, nothing. Never been drained.
The only maintenance has been replaced bearings on the boiler fan, replaced actuators on zone valves and 2 boiler services (if it ain't broke, don't fix it).
Anyway, this winter a few radiators have been slow to heat.
Yesterday morning I cleaned the F&E tank. It only had a thin layer of orange dust. No sludge. I then put in 2 litres of Sentinel X400 cleaner and I'm leaving it for a few weeks.
The pump has always been on setting 2, but yesterday afternoon I put it onto 3 and that caused the cooler rads to heat up better.
The pump isn't particularly noisy. It's probably noisier than it used to be, but if the 3 setting makes a big difference then perhaps it's getting weak.
Bearing in mind the F&E tank was fairly clean, I'm not expecting a lot of sludge in the system. Or am I wrong ? I'm cleaning and draining / flushing it anyway.
So, the pump is not noisy, but 15 years old and maybe not as muscular as it was once ... Would it be sensible to replace the pump when I drain in a few weeks ? Have I had my money's worth from this Wilo pump ?
I'm looking forward to hearing the voice of experience