Hi
I am a newbie here so here goes:
I have an open vented system 30 years old. Old house mix of old cast iron rads and newer ones- 18 in all. The system is divided by two zone valves into 1. Downstairs Bathroom, office, living room and hall 2. 2 bedrooms plus 3 public rooms downstairs and 2 upstairs plus upstairs bathroom. With circuit 1 ON and 2 OFF, system was sucking air from somewhere.
Pump ( new Grundfos 15/60 ) noisy with air. I bleed the air manually from the pipe at the top of the system - all goes quiet for a couple of hours. I put on both circuits 1 & 2 and all is quiet for hours but eventually the noise at the pump. Also from time to time I get overflow from balance tank in loft.
( Its a bungalow so loft is on same level as the bedrooms upstairs thus very little "head". Big old hot water storage tank, secondary hot tank with immersion heater, cold water storage to feed hot tank and CH balance tank mounted high as poss under rafters. All worked fine for 29years after piping down to 8mm from 2" and new boiler 1983
Boiler is an ideal Mex 26kw located in a downstairs utility / shower room. Top Flue through roof 4mtrs.
I know that the sytem has a fair amount of sludge and also black deposits ( seen on valves and pipe ends ) so last weekend I decided to put 2ltrs X800 in the system and run the system for 4 hours ( this after taking advice from Sentinel to run for 1 hour or up to a few days...and also reading many posts in favour of X800 left in for a few hours even without the power flush bit.)
Well after four hours - whole system running at normal temp. during which system is quiet as a mouse and running beautifully - no over pumping no pump noise....I drained down the system as per normal procedures etc. Disappointed that the outflow wasn't a really dirty sludgy colour....looked pretty clean- just a beige soapy stream and no sedimentary deposit left by the grid/drain either. So, fitted a brand new auto trickle air vent at top of system ( Italian float type - nice looking piece of kit )- the old bleed valve was clearly sludged up and quite rotten.... re-filled the system, added inhibitor, bled all the rads lowest first etc.and off we went.
With circuit 1 ON and 2 OFF, pump started to get noisy again, clicking in one of the rads ( air ) so sucking air from somewhere such that the trickle vent does not cope. Pump ( new Grundfos 15/60 last year ) noisy with air. I bleed the air manually from the pipe at the top of the system - all goes quiet for a couple of hours. I put on both circuits 1 & 2 and all is quiet for hours but eventually the noise at the pump ( which was installed on the RETURN all those years ago ) starts up again requiring me to manually vent again. ALSO for a long time been getting overflow from the balance tank in the loft. No contamination at all in the hot water, no discolouration, no taste, smell etc.( separate system but thinking of a coil issue if it has a coil - suspect its direct though - unless the small immerser tank DOES have a coil).
Is it the amount of sludge/crud in the system?? I have now bought 3 ltrs of X400 with the intention of starting again - leaving the X400 in the system for about 3-4 weeks??
Ideas/ suggestions please.
Many thanks
I am a newbie here so here goes:
I have an open vented system 30 years old. Old house mix of old cast iron rads and newer ones- 18 in all. The system is divided by two zone valves into 1. Downstairs Bathroom, office, living room and hall 2. 2 bedrooms plus 3 public rooms downstairs and 2 upstairs plus upstairs bathroom. With circuit 1 ON and 2 OFF, system was sucking air from somewhere.
Pump ( new Grundfos 15/60 ) noisy with air. I bleed the air manually from the pipe at the top of the system - all goes quiet for a couple of hours. I put on both circuits 1 & 2 and all is quiet for hours but eventually the noise at the pump. Also from time to time I get overflow from balance tank in loft.
( Its a bungalow so loft is on same level as the bedrooms upstairs thus very little "head". Big old hot water storage tank, secondary hot tank with immersion heater, cold water storage to feed hot tank and CH balance tank mounted high as poss under rafters. All worked fine for 29years after piping down to 8mm from 2" and new boiler 1983
Boiler is an ideal Mex 26kw located in a downstairs utility / shower room. Top Flue through roof 4mtrs.
I know that the sytem has a fair amount of sludge and also black deposits ( seen on valves and pipe ends ) so last weekend I decided to put 2ltrs X800 in the system and run the system for 4 hours ( this after taking advice from Sentinel to run for 1 hour or up to a few days...and also reading many posts in favour of X800 left in for a few hours even without the power flush bit.)
Well after four hours - whole system running at normal temp. during which system is quiet as a mouse and running beautifully - no over pumping no pump noise....I drained down the system as per normal procedures etc. Disappointed that the outflow wasn't a really dirty sludgy colour....looked pretty clean- just a beige soapy stream and no sedimentary deposit left by the grid/drain either. So, fitted a brand new auto trickle air vent at top of system ( Italian float type - nice looking piece of kit )- the old bleed valve was clearly sludged up and quite rotten.... re-filled the system, added inhibitor, bled all the rads lowest first etc.and off we went.
With circuit 1 ON and 2 OFF, pump started to get noisy again, clicking in one of the rads ( air ) so sucking air from somewhere such that the trickle vent does not cope. Pump ( new Grundfos 15/60 last year ) noisy with air. I bleed the air manually from the pipe at the top of the system - all goes quiet for a couple of hours. I put on both circuits 1 & 2 and all is quiet for hours but eventually the noise at the pump ( which was installed on the RETURN all those years ago ) starts up again requiring me to manually vent again. ALSO for a long time been getting overflow from the balance tank in the loft. No contamination at all in the hot water, no discolouration, no taste, smell etc.( separate system but thinking of a coil issue if it has a coil - suspect its direct though - unless the small immerser tank DOES have a coil).
Is it the amount of sludge/crud in the system?? I have now bought 3 ltrs of X400 with the intention of starting again - leaving the X400 in the system for about 3-4 weeks??
Ideas/ suggestions please.
Many thanks