tucker
Hi
I recently added a downstairs extension and in the process extended the central heating loop to add a new rad. I also changed a single for a double.
Prior to adding the rad I ran the system with some sentinal x4000 for 2 weeks to remove and sludge and then cleaned out the system, added inhibitor and re filled it. All the new pipework was exposed for several weeks, so I could check for leaks and all seemed well.
I've changed all but two of the rads over time now and those two are about 17 years old.
These two rads seemed fine, but over the past two months, one seems to be getting a build up of air and the other has gone cool at the botom. Both are upstairs.
I've bled the one with air about 5 times and over a 10 day period or so it has a little air in it again and the top isn't as hot as the bottom. I've also noticed the water is murky, despite me emptying it and flushing it out?
Boiler is a saunier duval Thermaclassic F30E combi and it's a closed system. The pump has a bleed valve on top which I've checked and it's open.
Any idea why I'm getting air? I've no obvious signs of any leak and can't see why any small amount of air isn't venting via the bleed on the pump.
Would replacing the two old rads be worth considering or have I not flushed it properly?
I recently added a downstairs extension and in the process extended the central heating loop to add a new rad. I also changed a single for a double.
Prior to adding the rad I ran the system with some sentinal x4000 for 2 weeks to remove and sludge and then cleaned out the system, added inhibitor and re filled it. All the new pipework was exposed for several weeks, so I could check for leaks and all seemed well.
I've changed all but two of the rads over time now and those two are about 17 years old.
These two rads seemed fine, but over the past two months, one seems to be getting a build up of air and the other has gone cool at the botom. Both are upstairs.
I've bled the one with air about 5 times and over a 10 day period or so it has a little air in it again and the top isn't as hot as the bottom. I've also noticed the water is murky, despite me emptying it and flushing it out?
Boiler is a saunier duval Thermaclassic F30E combi and it's a closed system. The pump has a bleed valve on top which I've checked and it's open.
Any idea why I'm getting air? I've no obvious signs of any leak and can't see why any small amount of air isn't venting via the bleed on the pump.
Would replacing the two old rads be worth considering or have I not flushed it properly?