Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Air in central heating system! in the Central Heating Forum area at Plumbers Forums

Status
Not open for further replies.
B

baronwills

Hi folks, hope you can help.

Going round to a customer tomorrow who says that every few weeks he bleeds his radiators and all the upstairs rads are full of air so he has to keep topping up the system. The boiler is in the garage, a 2yr old Worcester combi.

Not sure where to start looking so any advice would be gratefully recieved.
 
first check is it "air" or hydrogen which will burn as you bleed the rad ( if you light it! )
that would indicate excessive corrosion taking place.
check pipe work set up of fill and vent, height over f+e

just noticed its a combi, most likely never flushed out properly, corrosion
 
Last edited:
When was the system last drained/flushed through? Has inhibitor been added recently? Has the customer been filling the system without topping up the inhibitor? Fragments from inside the radiators could be reacting with other metals resulting in iron oxide in the system causing the air to build-up. Have a look at this link for a better description:

Radiator Troubleshooting - A L Plumbing And Heating
 
Status
Not open for further replies.

Similar plumbing topics

If you are paranoid, refill, circulate and...
Replies
2
Views
306
Can central heating / gas engineer expert help...
Replies
0
Views
824
B
Context for issue: I'd like to start by...
Replies
0
Views
561
Butchy10
B
It has dropped after isolating. Bugger
Replies
9
Views
835
Replies
3
Views
760
Back
Top