marsaday

I keep getting air coming into my bathroom towel rail. it needs bleeding every few days.

does this mean air is getting into the rad from somewhere ? i cant see any leaks.

i recently drained down and used this rad to add the inhibitor to it. then i refilled the system.

i also noticed on the boiler today the pressure had decreased from 1.2 to 0.7 bar because i bled the rad last week. only just noticed this decrease though.

any ideas if i have cocked up ?
 
no you have not cocked up. probably just excess air in system from drain down gradually working it's way round the system. just top the system back up to working pressure.
 
After re-filling a system the fresh water is airated & it can take anytime up till 3 weeks to completly rid itself of air so a slight pressure drop over this time is not too much to be concerned with.
 
Status
Not open for further replies.

Similar plumbing topics

  • Question
It could well be, the OP will soon hopefully...
2
Replies
35
Views
3K
  • Question
Red circles show my new AAVs and the manual...
Replies
17
Views
2K
  • Question
Hi Combi boiler, No escape from pressure...
Replies
3
Views
1K
  • Question
Fresh copper in a heating system will evolve...
Replies
1
Views
1K
S
  • Question
Hi guys, we moved into a place last Dec with...
Replies
0
Views
992
Sam Grocock
S
Back
Top