Went to a property earlier today, the vaillant ecotec has a variable flu kit installed. The outlet of the flu goes through the roof, the air inlet in inside a built in side way with a plastic roof. I at risked the boiler and want to send the relevant regulation to the client explaining what I have done. But where in the regs does it actually say that the air inlet has to come from outside?! I have found the following:
British Standard 5440-1:2008
Flueing and ventilation for gas appliances of rated input not exceeding 70 kW net (1st, 2nd and 3rd family gases) –
Part 1: Specification for installation of gas appliances to chimneys and for maintenance of chimneys
Regulation 10.2.1. Terminals
States:
"Terminals shall not be sited in covered passageways between buildings" THIS IS ONLY REFERRING TO THE TERMINAL which has a different definition to the "air supply duct"
Commentary:
When a terminal is to be sited in a car port or building extension the
following additional requirements apply:
1) the car port or other add-on extension should have at least two
open and unobstructed sides
AGAIN ONLY REFERS TO THE TERMINAL!!
Thank you very much for any help you can give
British Standard 5440-1:2008
Flueing and ventilation for gas appliances of rated input not exceeding 70 kW net (1st, 2nd and 3rd family gases) –
Part 1: Specification for installation of gas appliances to chimneys and for maintenance of chimneys
Regulation 10.2.1. Terminals
States:
"Terminals shall not be sited in covered passageways between buildings" THIS IS ONLY REFERRING TO THE TERMINAL which has a different definition to the "air supply duct"
Commentary:
When a terminal is to be sited in a car port or building extension the
following additional requirements apply:
1) the car port or other add-on extension should have at least two
open and unobstructed sides
AGAIN ONLY REFERS TO THE TERMINAL!!
Thank you very much for any help you can give