Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Air Pressure Fault - Heatline Boiler in the Boilers area at Plumbers Forums

Status
Not open for further replies.
Messages
2
Morning all,

We inherited a c.2007 Heatline Compact boiler when we moved into our house.

On Friday the boiler developed an air pressure fault. I first tested the air pressure switch in both the Common-normally closed and Common-normally open positions and both are working ok. I even tried a spare air pressure switch just in case.
Whilst the fan was operating on initial startup, I took it out for a clean and re-lubricated it which has sped it up a little.
I then Very briefly bypassed the air pressure switch to see if the boiler would fire up and it did. This suggests to me it’s not a PCB or ignition issue and must be something to do with the fan not creating a sufficient pressure differential to activate the APS.

The flue appears clear.

I’m still having the same fault come up.

I made some observations and had some thoughts and wanted to run them by this forum for advice. Firstly, some of the seals around the fan-flue connection are crumbling. Still fairly tight but how significant is that issue for an air pressure fault please. Generally how significant are the soundness of the seals around the flue and fan for air pressure faults?

Also, is there a way of determining whether my fan is spinning fast enough? Any tool I can use to assess speed or pressure within the fan unit?

Any other thoughts on what the issue could be would be greatly welcomed.Thanks all. Stay safe.
 
Stop playing inside a combustion appliance and get yourself a competent gas safe engineer.
 
Closed as it’s a gas appliance
 
Status
Not open for further replies.

Similar plumbing topics

M
I have a viessman vitodens 222F combi storage...
Replies
0
Views
548
Max Hill
M
P
Tricky situation for you. Boiler shouldn't...
Replies
2
Views
434
P
  • Locked
Doesn't matter, mod will remove or close it.
Replies
3
Views
834
Again, ongoing thanks. I'll have to get to my...
Replies
18
Views
2K
You have a blockage from a dirty system needs...
Replies
2
Views
2K
Back
Top