M
mattyp
Upon servicing this applaince today i noticed that one of the air pressure switch tubes was hanging off the venturi [ tube still attached to the switch] The boiler was working ok , i reconnected the tube and guess what ? the switch wouldnt operate !! The boiler would only work with one hose connected . I was of the understanding that if one of the tubes were not in place the switch would not work [ ive attended many faults with rotten hoses or splits etc ]?! It done the same with the case on or off . I tried to phone vokera but couldnt get through for 20 mins so gave up[ it was 4pm !] . The customer had a spare switch [dont ask why !] that i also tried, this also done the same thing ! Just wondered if any of you gas boys had come across this before ? The venturi is clean and the positive side of the switch is connected to the positive side of the fan , its the negative thats hanging off, ive tried swapping the hoses around etc but still no joy and it is deffo supposed to be on as i looked at the parts diagram that showed both hoses connected ! the heat exchanger is clean and the performance test was low as can be !