R
rab250
Been asked to have a look at an Alpha cd30s LPG boiler the other day that was locking out on startup. anyway after getting the boiler lit after a few resets i proceeded to check the pressure differentials for the burner pressure and they were way out also i stuck my fga in the sampling port and the co went to -OR- after quite a while trying to set the boiler up and checking the air sampling port ( which had 500ppm co ) i decided to change the flue and flue top seal.
I can now get the settings bang on on low ch which is .30 differential and 10%co2 and the fga readings are good too .0008 ratio, But as soon as i crank up to the ch max which is 4.16 differential the c0 goes through the roof. I feel as though somewhere the air/gas ratio is being affected but i dont know these boilers well enough and technical support have'nt been much help.
I am now at a loss with this boiler and anything else would be just throwing parts at it until its fixed which is something i dont like doing so i was wondering if anyone actually knows these boilers inside out that might have a valid suggestion.
I can now get the settings bang on on low ch which is .30 differential and 10%co2 and the fga readings are good too .0008 ratio, But as soon as i crank up to the ch max which is 4.16 differential the c0 goes through the roof. I feel as though somewhere the air/gas ratio is being affected but i dont know these boilers well enough and technical support have'nt been much help.
I am now at a loss with this boiler and anything else would be just throwing parts at it until its fixed which is something i dont like doing so i was wondering if anyone actually knows these boilers inside out that might have a valid suggestion.