Hi - I have a curious little problem which is now costing me every spare minute and lots of phone calls which I feel needs sharing before i go mad. I have moved an Alpha HE CB25 ten feet from one wall to another no problems and the only addition was a plume managment kit which is as MI. Since then when the boiler comes up to temperature in either DHW or heating the A & B lights will flash together for around 10secs then it will happily reset itself and carry on for another 1min before same happens again - MI says flue or fan fault....thanks
Whats been done so far after becoming best friends with alpha tech help
1 replaced the fan - same
2 removed the plume kit - same
3 removed the flue restrictor - same (wasnt in instructions)
4 replaced the primary temp sensor
5 measured everything from NTC at varying temp to fan voltage to burner pressure DHW & heating APS so am loathed to replace pcb as it all measures up - same
6 removed the entire boiler from the wall and replaced the condense hose as look kinked - same
7 cleaned out the condense trap and routed to a bucket to check not blocked - same
8 removed the condensing heat exchanger and checked for block/cracks - same
9 checked system water quality - clean
The only indication that its about to lock out is a slight bubbling sound as if water vapour is stuck in the flue Customer has said in heating mode they dont notice it as room stat temp in house is kept quite low but on full blow when showering it keeps cutting out & shower goes cold & i get a call each and everytime.???
Whats been done so far after becoming best friends with alpha tech help
1 replaced the fan - same
2 removed the plume kit - same
3 removed the flue restrictor - same (wasnt in instructions)
4 replaced the primary temp sensor
5 measured everything from NTC at varying temp to fan voltage to burner pressure DHW & heating APS so am loathed to replace pcb as it all measures up - same
6 removed the entire boiler from the wall and replaced the condense hose as look kinked - same
7 cleaned out the condense trap and routed to a bucket to check not blocked - same
8 removed the condensing heat exchanger and checked for block/cracks - same
9 checked system water quality - clean
The only indication that its about to lock out is a slight bubbling sound as if water vapour is stuck in the flue Customer has said in heating mode they dont notice it as room stat temp in house is kept quite low but on full blow when showering it keeps cutting out & shower goes cold & i get a call each and everytime.???