Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Are Oil pipe inserts regulation or not ? in the Boilers area at Plumbers Forums

Status
Not open for further replies.
Messages
23
Hi guys , i got my oftec inspection next week .any advice ??
Has anyone else had inspection ?
Hes coming to inspect an install .
Someine has told me that i need to use oil pipe inserts every time .is this true ??
 
Oftec do recommend oil pipe inserts while making compression joints, thats what i was told by oftec training northern ireland. I check oftec files for you and get back to you.
 
image.jpeg
image.jpeg hope this helps
 
Yes it is. Got told off by Oftec inspector myself. They prefer if you used flared fitting rather than compression. Have used them ever since. Look at BES.co.uk where you can mail order them and get the tool and fittings you need. Its similar to what is used on brake lines on cars.
 
on my inspection this subject came up, yea use inserts with compression fittings.
 
If you are serious about your work and customers and adhere to the rules and regs you won't go wrong. Do your homework and training and it will be a piece of cake. Cut corners like some and it ain't gonna work!
As mentioned inserts are used on soft copper but we use flared fittings where possible.
 
you would struggle to find an insert on an oil line with a compression fitting here in Antrim - seriously think I am only one using them
 
To be honest, I think the OFTEC written guidance sits on the fence a bit as regards inserts. On the page before the one that Gazzt posted at the top it just talks about the problems that Type A compression fittings can cause and then refers to BS EN 1254 Part 2. The BS says that inserts are required on R220 (soft) tube at 18mm and above and are possibly required below 18mm, manufacturer's advice should be sought. Manufacturer's advice seems a bit more definitive - e.g Connex say 'when using compression fittings with soft copper tube...it is essential that an appropriate tube liner is also fitted.' It would be easier if the Oftec guidance just said 'inserts should be used'.
 
I use inserts for my personal preference they help support soft copper and help make a good compression joint, so i can be confident that i have done my best at preventing oil leaks.
 
To be honest, I think the OFTEC written guidance sits on the fence a bit as regards inserts. On the page before the one that Gazzt posted at the top it just talks about the problems that Type A compression fittings can cause and then refers to BS EN 1254 Part 2. The BS says that inserts are required on R220 (soft) tube at 18mm and above and are possibly required below 18mm, manufacturer's advice should be sought. Manufacturer's advice seems a bit more definitive - e.g Connex say 'when using compression fittings with soft copper tube...it is essential that an appropriate tube liner is also fitted.' It would be easier if the Oftec guidance just said 'inserts should be used'.

Truth is OFTEC just want to create large books full of nonsense to make OFTEC look professional and to make exams harder.
Plain, compressed, sensible wording would be better
 
Status
Not open for further replies.