Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss ariston storage combi in the Plumbing Jobs | The Job-board area at Plumbers Forums

Status
Not open for further replies.
B

buckley plumb

had a quick look at an old ariston storage combi for a friend today it was massive .lh heating prv constantly dripping - decided to put boiler on to see if it worked - topped to 1 bar just slight drip from prv at 2 bar so prv passing after being on for 5 min at 2 bar rads got warm the prv gushing out but pressure still 2 bar heard cold mains hissing it was passing into the boiler even with the filling loop removed so assume plate has had it . never knew ariston did a storage combi . advised customer to get new boiler .
 
that's the one steve massive and parts are realy expensive.
 
They have a small unvented stuck on the side of them yeh? was it that prv that was passing?
 
no mate the heating one topped to 1.5 bar and turned on all was ok just small drip then after 5 min it was gushing out but still on 2 bar turned boiler off and could hear mains water entering the boiler through cold connection and it was exiting throught heating prv . mains turned off boiler wnt to zero but turn mains on it filled its self to 2 bar and filling loop was off
 
Sounds like an expensive repair :) Do they still have a phex? Can't remember off hand and can't be chuffed to download the mi's :) Just thinking it'd most likely be that if they did have?
 
they are getting british gas out on fixed charge repair they say - been told if they cant fix it they wont charge . told them to ask for a quote as well then compare mine to it .
 
Status
Not open for further replies.

Similar plumbing topics

Expansion vessel undersized, blocked flexi to...
Replies
1
Views
769
  • Locked
Thread Closed As Ops Gas Safe Membership Has...
Replies
17
Views
2K
Thought I would update this since folks took...
Replies
9
Views
4K
sounds very much like expansion vessel,
Replies
23
Views
2K
I would bet that's a leaker Bottom of heat...
Replies
5
Views
1K
Back
Top