Ariston under sink heater, help!!!! | Plumbing Jobs | The Job-board | Plumbers Forums
  • Welcome to PlumbersTalk.net

    Welcome to Plumbers' Talk | The new domain for UKPF / Plumbers Forums. Login with your existing details they should all work fine. Please checkout the PT Updates Forum

Welcome to the forum. Although you can post in any forum, the USA forum is here in case of local regs or laws

American Visitor?

Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Ariston under sink heater, help!!!! in the Plumbing Jobs | The Job-board area at Plumbers Forums

Status
Not open for further replies.

Riley

Plumbers Arms member
Plumber
Gas Engineer
Subscribed
Messages
10,833
Morning all

trying to fit an undersink water heater for custard in a flat.

Only position for it is in like an old airing cupboard in the centre of the property in the bathroom.

Now ive just spoken with ariston as I wasn't sure about PRV termination and they don't endorse termination through waste pipe. I'm really confused as ive seen loads of these and cylinders terminated via a hepvo into waste. Were these installs all wrong or was the guy at ariston talking rubbish?
 
Last edited:
G3 Regs let us use HEPvO valve for unvented hot water discharge as long as it’s acceptable by your local Building Control.
 