Interested on thoughts on this (I've also posted on another forum but thought this might be a better place to ask);
Long time lurker, have gleamed some great knowledge from this site, finally signed up as I cant find an exact answer to the below. I'm not a heating engineer, but an electrical engineer that has mostly sussed how the current system works (feel free to correct any understanding/terminology below).
I'm at a stage in house renovation where it would be least disruptive to do this, I'm interested on thoughts on the following as its gone around in my head too many times.
I've got a 14kw (4kw elec) ecodan (monobloc) ASHP, I've reduced the energy use from 15Mwh down to 12MWh per year (there was a fault) and then further down to just under 9MWh per year by splitting into 3 zones -one per floor and a couple of other improvements).
Additionally, I've got a 6KW log burner in the lounge (no back boiler)
In the back of my head I'm wondering if I can make it yet more efficient to run by utilising a back boiler on the log burner in the lounge.
There isn't a buffer tank on the system and it has a single coil 210L tank for DHW. CH flow temp is weather compensated, HW kept at 55 deg c.
My thoughts are, 28mm run to log burner with back boiler in lounge (on a pumped system) and install a buffer tank (size a bit of an unknown 100-150L?) on the return feed to ashp after the 210L tank and situated next to it.
Originally I thought of a twin coil tank, but this wouldn't allow the heat from back boiler to be used on the CH circuits without interfering with weather compensation/cooling the HW.
After a bit more thought, this is where I'm trying to figure things out in my head.
Preferably the back boiler circuit would be unvented but I'm now aware of the issues with uncontrolled heat source etc here 2 tiers of safety required.
In my head, the ASHP return feed would run through the coil in the buffer tank (reducing the extra glycol volume).
Back boiler circuit would use towel rail (and maybe rad) in the bathroom (which it passes en route) as a heat leak.
Ideally the towel rail would also be then free to be used during summer months without circulating water back thru the now cold back boiler using the heat in buffer tank which at that point would be heated by ASHP.
This has all come about (apart from rising elec costs) as I have been speccing a generator that can run the heat pump if/when the rolling blackouts start.
I could get away with a much smaller generator to just run the pumps and controls, if there was an alternative source of heat.
Log burner gets used for approx. 5-6 hours a day from September through to March, there would be something quite satisfying about lighting at 4pm and knowing that the energy is being used in other rooms of the house in the meantime / amount the ASHP comes on for is being reduced. The "new" log burner/back boiler I've considered is a Coalbrookdale Severn. Bonus would be getting over the dilemma of making towel rad warm in summer without an elec element.
Not asking for a design as such here, aware of G3, Hetas etc and concerns you guys may have. I'm intrigued to know how it would best be done / if it could be done with a unvented buffer with additional safety measures, and more importantly, if it would be worth it or has anyone done something similar?
If it was a vented "buffer", would I be correct with ASHP return indirectly heating the buffer tank, which stores the (directly heated) water from the pumped back boiler/towel rad circuit. This would then have a F/E tank in loft above it/ sufficiently high up in airing cupboard (prefered).
Laddomat 21 has come up in my research as being a good idea to prevent the stove getting too cold when initially lit.
There's probably something huge that I've missed here (towel rad running at crazy temps, actual energy calcs give a 30 year pay back etc)
Cheers!
(can attempt to draw a pic/diagram if it helps)
In summary -
Existing ASHP and dhw tank.
Add back boiler circuit in which is indirectly connected to ASHP flow/return circuit.
Try and get all of it into airing cupboard.
Enjoy added benefits of buffer for ASHP.
Get around the towel rad in summer issue,
Sit back and enjoy the feeling of utilising all heat instead of wasting a lot of the log burner output.
Rough level of work required so that I can weigh up if its worth it/amount of kit required/space it might take up.
Long time lurker, have gleamed some great knowledge from this site, finally signed up as I cant find an exact answer to the below. I'm not a heating engineer, but an electrical engineer that has mostly sussed how the current system works (feel free to correct any understanding/terminology below).
I'm at a stage in house renovation where it would be least disruptive to do this, I'm interested on thoughts on the following as its gone around in my head too many times.
I've got a 14kw (4kw elec) ecodan (monobloc) ASHP, I've reduced the energy use from 15Mwh down to 12MWh per year (there was a fault) and then further down to just under 9MWh per year by splitting into 3 zones -one per floor and a couple of other improvements).
Additionally, I've got a 6KW log burner in the lounge (no back boiler)
In the back of my head I'm wondering if I can make it yet more efficient to run by utilising a back boiler on the log burner in the lounge.
There isn't a buffer tank on the system and it has a single coil 210L tank for DHW. CH flow temp is weather compensated, HW kept at 55 deg c.
My thoughts are, 28mm run to log burner with back boiler in lounge (on a pumped system) and install a buffer tank (size a bit of an unknown 100-150L?) on the return feed to ashp after the 210L tank and situated next to it.
Originally I thought of a twin coil tank, but this wouldn't allow the heat from back boiler to be used on the CH circuits without interfering with weather compensation/cooling the HW.
After a bit more thought, this is where I'm trying to figure things out in my head.
Preferably the back boiler circuit would be unvented but I'm now aware of the issues with uncontrolled heat source etc here 2 tiers of safety required.
In my head, the ASHP return feed would run through the coil in the buffer tank (reducing the extra glycol volume).
Back boiler circuit would use towel rail (and maybe rad) in the bathroom (which it passes en route) as a heat leak.
Ideally the towel rail would also be then free to be used during summer months without circulating water back thru the now cold back boiler using the heat in buffer tank which at that point would be heated by ASHP.
This has all come about (apart from rising elec costs) as I have been speccing a generator that can run the heat pump if/when the rolling blackouts start.
I could get away with a much smaller generator to just run the pumps and controls, if there was an alternative source of heat.
Log burner gets used for approx. 5-6 hours a day from September through to March, there would be something quite satisfying about lighting at 4pm and knowing that the energy is being used in other rooms of the house in the meantime / amount the ASHP comes on for is being reduced. The "new" log burner/back boiler I've considered is a Coalbrookdale Severn. Bonus would be getting over the dilemma of making towel rad warm in summer without an elec element.
Not asking for a design as such here, aware of G3, Hetas etc and concerns you guys may have. I'm intrigued to know how it would best be done / if it could be done with a unvented buffer with additional safety measures, and more importantly, if it would be worth it or has anyone done something similar?
If it was a vented "buffer", would I be correct with ASHP return indirectly heating the buffer tank, which stores the (directly heated) water from the pumped back boiler/towel rad circuit. This would then have a F/E tank in loft above it/ sufficiently high up in airing cupboard (prefered).
Laddomat 21 has come up in my research as being a good idea to prevent the stove getting too cold when initially lit.
There's probably something huge that I've missed here (towel rad running at crazy temps, actual energy calcs give a 30 year pay back etc)
Cheers!
(can attempt to draw a pic/diagram if it helps)
In summary -
Existing ASHP and dhw tank.
Add back boiler circuit in which is indirectly connected to ASHP flow/return circuit.
Try and get all of it into airing cupboard.
Enjoy added benefits of buffer for ASHP.
Get around the towel rad in summer issue,
Sit back and enjoy the feeling of utilising all heat instead of wasting a lot of the log burner output.
Rough level of work required so that I can weigh up if its worth it/amount of kit required/space it might take up.