Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Automatic bypass and radiator thermostatic valves in the UK Plumbers Forums area at Plumbers Forums

Messages
106
Hi

If the radiator valves are not demanding much heat and are near closed then the automatic bypass should be cutting in.

I have a few queries that may be obvious but not to me as old system did not have an automatic bypass.

[1] When it comes in it is shunting some of the hot water, will this not mean that the zones that do want a bit of heat are robbed of it?
[2] When it comes in and it starts to get hot (shunting the water) will the boiler not see a higher return temperature and think it needs less heat (or stops the burner) again meaning no heat for the near closed valves that require some heat?
[3] When it does cut in, how hot is it supposed to get?
[4] When it does come in then it seems noisy as the water is gushing through it - is this normal?

At the moment I have set it high and using open radiator instead (but that will be upping the gas costs so I would like to get the bypass working correctly).

Thanks
Colin
 
Last edited:
These type of systems are difficult to configure Mr Evil is more experienced and has the benefit of fitting it and having it installed, I would be guided by him there is such a low kw demand at times with evo home, modern boilers which have a low water content and move the system water quickly struggle to get going as there's no where for it to go, even when the auto bypass kicks in it doesn't drop the temperature it's like driving your car in 1st gear at 5mph , I very much doubt Worcester will be any help they would be guiding you to use their controls and weather compensation which in my experience is the way to go .
 
Put a few pictures up Colin of the boiler and bypass set up ??
Hi

Pictures of boiler and bypass.

The bypass loop goes to where the cylinder is and is approx 20m from boiler to cylinder so total length ~40m?

Thanks
Colin
 

Attachments

  • Bypass.jpg
    Bypass.jpg
    498 KB · Views: 44
  • Boiler_.jpg
    Boiler_.jpg
    457 KB · Views: 42
System boiler ?? Where's your pump ?
Hi

I am not sure what you are asking, the boiler (from the installation and maintenance instructions) is a 30KW Greenstar 8000 Life gas fired condensing system boiler.

As far as I know there is no pump other than that built into the boiler (or if there is one external I cannot see/find it).

Thanks
Colin
 
Last edited:
I just needed to confirm you had a system boiler with a internal pump.
1 - your boiler is a range rated appliance meaning when it leaves the factory it set to full rate , when it was installed did the engineer adjust the heat output and pump curve to suit you system ? If not then your boiler will be Operating at Full rate the pump will be running at 400 mbar constant as the chart below.
2 - I recommend you reduce the kw output to 15 kw and pump curve to 2.0m of head as a starting point and monitor it's performance increase this gradually over the winter heating period if needed.
3 - reducing the output will save on gas , a lower pump head speed will quieten the system and take the pressure off the boilers internal components and reduce wear and tear.
Please study the attached tables below which are taken from your Installation manual and talk to your installer to see if adjustments have been made ? .

Regards kop
 

Attachments

  • Screenshot_20211014-100940.png
    Screenshot_20211014-100940.png
    229.7 KB · Views: 31
  • Screenshot_20211014-101237.png
    Screenshot_20211014-101237.png
    214.1 KB · Views: 30
  • Screenshot_20211014-101258.png
    Screenshot_20211014-101258.png
    207.7 KB · Views: 34
  • Screenshot_20211014-062338.png
    Screenshot_20211014-062338.png
    343.2 KB · Views: 33
I just needed to confirm you had a system boiler with a internal pump.
1 - your boiler is a range rated appliance meaning when it leaves the factory it set to full rate , when it was installed did the engineer adjust the heat output and pump curve to suit you system ? If not then your boiler will be Operating at Full rate the pump will be running at 400 mbar constant as the chart below.
2 - I recommend you reduce the kw output to 15 kw and pump curve to 2.0m of head as a starting point and monitor it's performance increase this gradually over the winter heating period if needed.
3 - reducing the output will save on gas , a lower pump head speed will quieten the system and take the pressure off the boilers internal components and reduce wear and tear.
Please study the attached tables below which are taken from your Installation manual and talk to your installer to see if adjustments have been made ? .

Regards kop
Hi

Thanks for the reply and advice.

The default for the boiler is constant pressure 250mbar (3-d1) and the default min output (5-A3) is 10% (this has had to be increased to 20% to work correctly with the control system I have).

The house will need access to at least 25KW if all radiators fully on and open, even more if hot water for cylinder comes on at same time. The boiler starts at the lowest output (20% of 30 => 6KW) and remains there for quite a while before bumping up its modulation - slow start mechanism)

I am not sure where the setting for 2.0 m of head is in the manual.

Thanks
Colin
 

Attachments

  • Greenstar_8000_Life_System_Installation_and_Maintenance_Instructions.pdf
    18.9 MB · Views: 42
Last edited:
Think 25 kw is to high , time your hot water heat up at different times to your heating , your rads will not be calling for full heat that often what's the minimum night time set back temperature. I don't advise lower than 12°c it better to be on a bit longer at a lower rate
Kop
 

Attachments

  • Screenshot_20211014-211703.png
    Screenshot_20211014-211703.png
    195.1 KB · Views: 23
  • Screenshot_20211014-211411.png
    Screenshot_20211014-211411.png
    223.4 KB · Views: 30
  • Screenshot_20211014-211442.png
    Screenshot_20211014-211442.png
    220.7 KB · Views: 27
  • Screenshot_20211014-211452.png
    Screenshot_20211014-211452.png
    93.2 KB · Views: 39
Hi

The min temperature is 16 degrees

Thanks
Colin
Think your pretty much there Colin it's just fine tuning, the only other form of control you Could consider is weather compensation? this gives control over the heating pump as stated in the installation manual I doubt it will work as intended though two forms of control rarely configure well ? but Mr Evil is our go to for Honeywell Evo home . Regards kop
 
Last edited:
Think your pretty much there Colin it's just fine tuning, the only other form of control you Could consider is weather compensation? this gives control over the heating pump as stated in the installation manual I doubt it will work as intended though two forms of control rarely configure well ? but Mr Evil is our go to for Honeywell Evo home . Regards kop
Hi Kop

Many thanks for you help and advice

Regards
Colin
 

Similar plumbing topics

  • Question
Yes, unless you are prepared to suffer with...
Replies
16
Views
2K
S
  • Question
Sketch of layout required to make sense of...
Replies
1
Views
1K
Hi Tony How did you get on with your diverter...
Replies
1
Views
361
  • Question
Will be a 15-60 then prob ups2 Green lights ?
Replies
8
Views
933
  • Question
Yes, just take your time, the only downside of...
Replies
14
Views
3K
Back
Top