50/70kw Danesmoor locking out every 4 to 5 months.Diffuser seems to be sooted blocking pc.Last set up Feb 18.
A/temp 7c
Co2 11.8
Co 24ppm
Oil 155psi with danfos s 1.75 60s.
looked like afterburn so changed solenoid.
Back today to clean diffuser again.
Electrodes 4/5mm apart.1/2mm in front of nozzle .All per M.Is.
Been servicing this boiler for 18years with no faults until now.
Oil pressure steady,clean oil supply and visual inspection of flame is perfect.Oil vacuum and flue draught perfect.Intensive service carried out Feb 18.
My next step might be an oil pump or check nrv before nozzle.
Back in Feb i used a kane 455 and Testo 327-1 and got same resaults.
This has been going on for approximately two years so any help would be great.
A/temp 7c
Co2 11.8
Co 24ppm
Oil 155psi with danfos s 1.75 60s.
looked like afterburn so changed solenoid.
Back today to clean diffuser again.
Electrodes 4/5mm apart.1/2mm in front of nozzle .All per M.Is.
Been servicing this boiler for 18years with no faults until now.
Oil pressure steady,clean oil supply and visual inspection of flame is perfect.Oil vacuum and flue draught perfect.Intensive service carried out Feb 18.
My next step might be an oil pump or check nrv before nozzle.
Back in Feb i used a kane 455 and Testo 327-1 and got same resaults.
This has been going on for approximately two years so any help would be great.