Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Back boiler - electrics in the Boilers area at Plumbers Forums

Status
Not open for further replies.

anz

Plumbers Arms member
Plumber
Gas Engineer
Messages
1,085
Went to a back boiler last week (Baxi Bermuda 50/4E) .

Newly bought property. Gravity hot water, cylinder stat, pumped heating, room stat. Two channel clock.

When calling for demand on the programmer and stat, the switched live to the boiler is not switching live.

The programmer is a Drayton LP522, there is L N E and two wires going to hot water on and heating on. Nothing else.

Should there be a link to live in one of the connections?

What tests can I do to work out what's wrong?

Link to programmer instructions: http://www.google.co.uk/url?sa=t&rc...6TCqB6zOHBjB6Gw&bvm=bv.73373277,d.d2k&cad=rja
 
Last edited:
The red light lights up, when calling for heating.

Room stat has live neutral and a switch wire. The switch does not go live, when clock is calling.
 
Does the switch live go live when you turn the stat up to call for heat?
 
Can you not link a live to the boiler to see if it fires up? then surely you can prove the time if fubard?
 
Yes the boiler definitely works, with controls linked out
 
Switch live remains dead, when all controls calling for heat
 
Does the switch live TO the stat FROM the programmer become live when you select HTG on the programmer?
 
Then the programmers knackered. Take the programmer off leaving the backplate and the wiring. Then link permanent live to whichever wire is heating on. Then you should have power AT the stat, this will then prove it's the programmer.
 
Sounds like it could be the case, I'll try that, going back Wednesday.
 
Power has to go through clock stat n pump then boiler last. If no power at stat then programmer goosed . Most of the back plates for the programmer are universal so i carry spare face just to test.
 
Status
Not open for further replies.

Similar plumbing topics

S
Boiler Fault I’m hoping someone can help with...
Replies
0
Views
114
S
  • Locked
Many thanks for everyone's help.