Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss back boiler ventilation in the Boilers area at Plumbers Forums

Status
Not open for further replies.

billybob150811

Plumbers Arms member
Plumber
Gas Engineer
Messages
526
vent is in floor don't think its ducted Is it AR to be honest its going to be difficult to explain to this old boy why he has had it serviced year after year and no one has mentioned the vent being an issue so if its not AR I will let it pass
 
I'd give him a polite notice suggesting he has it sorted !

Ducting the supply/combustion air is due to preventing Radon gas from ground entering his property.

It ( Radon), is linked to lung cancer. It creates radioactive dust which we breath in.

The vent which is open to below the floor could bring the gas into his home. If it isn't ducted.

It is a health risk ! If the gas is present. You can get information online regarding where about's in the UK the higher concentrations are
 
Last edited:
Venting through the under floor space is an acceptable method.

Make certain the vent is permanent. Check there is sufficient outside
air coming in to the under floor area.
 
Venting through the under floor space is an acceptable method.

Make certain the vent is permanent. Check there is sufficient outside
air coming in to the under floor area.
 
Floor ventilation for open flue appliances does not have to be ducted. Only flueless requires ducted ventilation through floors, and if room doesnt go direct to outside air - then ducted through rooms too.
 
Status
Not open for further replies.

Similar plumbing topics

Thanks for both replies - so the search is on...
Replies
2
Views
588
E
It sounds like that needs to be sealed from...
Replies
3
Views
1K
Something as simple as turning the power off...
Replies
12
Views
2K
We've just sorted one of these situations...
Replies
9
Views
1K
Hi appreciate and thanks to all that replied...
Replies
11
Views
1K
Back
Top