Apologies if this has been covered elsewhere but I can't find an answer to my questions.
I have a back boiler and gas fire which h has been serviced regularly over the years by different engineers with no issues.
Last time , the guy wanted to condem it due to not being compliant with the regulations. I've tried to look this up myself but am having difficulty. I'd be massively grateful for some advice.
There are supposedly three issues, vent too small, wrong flue, boiler compartment not sealed.
Fire is Housewarmer legend, max input 6.74kw (assume gross so 6.12 net).
Boiler is housewarmer 55 max input 21.5kw (assume gross so 19.6 net)
Total is 25.72. Vent area = 25.72x5= 128cm2.
My vent hole is 12x20 = 240cm2 but has a grille on outside and inside. Outside has very large holes with very thin bars so I am sure it will be at over the 128 needed.
Cover on the inside is too small. I looked it up and it's 68cm2 due to the grille pattern.
So can I just replace the internal grille to allow more airflow? The guy seemed to think the actual hole size was too small not just the grille. Have I done the calculations correctly?
Secondly he said that I need a double sleeved flue so air can pass up and down. I thought this was for combi boilers. It just has an aluminium flue going up the chimney which as far as I can tell is OK.
Thirdly, he said that the boiler compartment should be sealed and to be fair you can see the boiler through a gap on the other side of the wall. There is a cupboard there and if you open the door you can see the boiler compartment. There is a gap where the outer compartment houses the flue, so not a hole in the flue itself. As I can see the boiler through the gap, I agree with him on that one but I don't know why is wasn't picked up before.
My plan is to cut some ply to size and seal is all off with no more nails or similar. Would this acceptable?
Thanks for any help with this. I am scared to get someone in to take a look in case they condem it and I can't deal with that right now.
Cheers Edward
Apologies if this has been covered elsewhere but I can't find an answer to my questions.
I have a back boiler and gas fire which h has been serviced regularly over the years by different engineers with no issues.
Last time , the guy wanted to condem it due to not being compliant with the regulations. I've tried to look this up myself but am having difficulty. I'd be massively grateful for some advice.
There are supposedly three issues, vent too small, wrong flue, boiler compartment not sealed.
Fire is Housewarmer legend, max input 6.74kw (assume gross so 6.12 net).
Boiler is housewarmer 55 max input 21.5kw (assume gross so 19.6 net)
Total is 25.72. Vent area = 25.72x5= 128cm2.
My vent hole is 12x20 = 240cm2 but has a grille on outside and inside. Outside has very large holes with very thin bars so I am sure it will be at over the 128 needed.
Cover on the inside is too small. I looked it up and it's 68cm2 due to the grille pattern.
So can I just replace the internal grille to allow more airflow? The guy seemed to think the actual hole size was too small not just the grille. Have I done the calculations correctly?
Secondly he said that I need a double sleeved flue so air can pass up and down. I thought this was for combi boilers. It just has an aluminium flue going up the chimney which as far as I can tell is OK.
Thirdly, he said that the boiler compartment should be sealed and to be fair you can see the boiler through a gap on the other side of the wall. There is a cupboard there and if you open the door you can see the boiler compartment. There is a gap where the outer compartment houses the flue, so not a hole in the flue itself. As I can see the boiler through the gap, I agree with him on that one but I don't know why is wasn't picked up before.
My plan is to cut some ply to size and seal is all off with no more nails or similar. Would this acceptable?
Thanks for any help with this. I am scared to get someone in to take a look in case they condem it and I can't deal with that right now.
Cheers Edward