Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Balancing Radiators Thread. in the UK Plumbers Forums area at Plumbers Forums

D

Dotty

How To Balance Radiators

Tool List:

Radiator-bleeding key
Lockshield valve adjuster or adjustable spanner
Screwdriver
Digital thermometer or multimeter with thermometer function

1. Make sure all the radiators have been bled. Turn off the central heating and allow the radiators to cool.

2. Familiarise yourself with the valves. The lockshield will usually have a push-on cap or one that is secured with a screw through the top. Remove it.

3. Older models will have a wheelhead valve on the other side — used to turn the radiator on/off.

4. Newer radiators will have a thermostatic valve instead of a wheelhead valve.

5. Open up the valves on all the radiators in the house by turning them anti-clockwise.Wheelhead and thermostatic valves can be turned easily by hand, but the lockshield will need a plastic adjuster to open it up. These come with new lockshield valves. A spanner will also do the job.

6. Turn the central heating back on and note down the order the radiators heat up. Those nearest the boiler normally get hot first. If you’ve got a lot of radiators, get assistance. Turn the heating off and wait while the radiators cool down. You will also need check your DHW Cylinder primaries to ensure that the flow heats up at about the same rate as the heating flow. You should have a throttle valve on the primary return.

7. When the radiators are cool, switch the heating back on and go to the first radiator on your list. Turn the lockshield valve clockwise until it is closed and then open it by a quarter of a turn. Once the radiator has warmed up, take a temperature reading at the pipework leading to one of the valves.

8. Now take a temperature reading at the pipework leading to the other valve and open the lockshield valve gradually until there’s a 12°C difference between now and the reading you took in step 7 (allow a couple of minutes after each adjustment for the temperature to change). The temperature figures indicated in the last step and this one are relevant to the radiator shown – don’t take them as any kind of optimum figure – it’s the 12°C difference in temperature at the valves that counts. Next, check the rest of the radiators in the system following the order in the list. The further you move away from the boiler, you’ll find the lockshield valve will have to be opened more. The last radiator may need to have the lockshield valve fully open to work at full efficiency. Your radiators are now balanced and should work perfectly.

Getting A Temperature

A key part of this job is measuring the temperature difference across each radiator. Specially designed thermometers that strap round the pipes at either end of the radiator are available to buy or hire, but it’s not really necessary to use these. You can get away with a single digital thermometer — it just means that you can’t take simultaneous readings and you’ll have to move from one end of the radiator to the other.

Digital thermometers are available from around £10. Alternatively, some digital multimeters have a temperature sensor function. A digital multimeter with temperature function costs from £25 and can also be used for taking electrical readings and checking continuity in wires, among dozens of other functions.
 

Attachments

  • How To Balance Radiators.txt
    3.2 KB · Views: 121
This is a brilliant post from 2016! Still applies today. Bleeding radiators will be a thing for a good while yet. Not sure what central heating technologies will be knocking about in the future but we are a long way off.
 
As for measuring the temps of rads when balancing them I would suggest using an infrared thermometer gun for ease and convenience. They are sold on Amazon ranging from a tenner up to multiple hundreds of pounds.
 

Similar plumbing topics

  • Question
It’s expansion and contraction do you have the...
Replies
1
Views
524
  • Question
Will be a 15-60 then prob ups2 Green lights ?
Replies
8
Views
929
  • Question
The pin is in the part of the valve still...
Replies
10
Views
934
  • Question
The idea of balancing the system is to ensure...
Replies
2
Views
2K
  • Question
Best to remove the rad and put a hose pipe on...
Replies
5
Views
726
Back
Top