Can anyone tell me what is the max length of a 40mm bath waste running into a 110mm stack before I have to up-size to 50mm?:confused:

KW London
 
On a single stack max length of 40mm should be no more than 3m
 
Thanks guys, wastes are just on 3m so we should be inside tolerances.
 
The answer that it doesn't matter is wrong!!!! The limit is 3.0m beyond this (or if you have problems) you should consider installing some method of ventilating the pipe IE running an additional pipe to allow air into the system to prevent the foramtion of a vacuum in the pipe as water flows through it or putting an air admittance valve in the system. With 50mm pipe you only allowing an additional 1m (limit 4m).
 
hi was just wondering even if the nearest stack was say 5 metres away and 4 being longest point for the waste on the bath (when upped to 50mm pipe). what is the solution
a whole new stack ?
 
tees with 1/1/2 durgos in line to entrain air into the run. We did a very large house that had a ring beam plate steel grid on top floor so all wastes had to been run above the floor and the architects decided they didnt want to see soilpipes on the front of building. Same silly twats or won designer of the year on C4 Grand designs by the way. We had 50mm runs in excess of 7 mtrs and all worked fine.
 
if you cant get you r tolerances on a single stack system then you need to adjust to single stack modified!
The problem i see with durgos (although i do use them when i have to ) is that not inly do you need air to enter the system but also exit!! a durgo has non return so how can air escape if need be to give an equal positive nad negative pressure in the pipe work??
I can t see the main stack vent doing this as although it is 4" to the termination its axillary purpose is to vent the manhole hence such a large termination. Most fixture unit rating on a domestic property could really se you use a 50mm stack vent but venting the manhole prevents this!
 
hi , if 40mm max length is 3 meters
and if 50mm max length is 4 meters

can a bath have 2.5 meters of 40mm and joint and then 3.5 meters of 50mm?? giving total 6 meters?
 
Check Building Regs approved document H, it says you can use an anti vac or resealing trap if the runs are longer than stated.
 
Clearly if you can only run 4m of 50mm then can't run 6m of mixed 50mm and 40mm. Still think the antivac trap is the best option and run as much as you can in 50mm this should avoid any problems.
 
Status
Not open for further replies.

Similar plumbing topics

  • Question
Best thing to do first is to read the relevant...
Replies
1
Views
549
B
  • Question
Thank you but any chance of a link or picture...
Replies
4
Views
358
  • Question
Minimum size should match the trap, if it’s...
Replies
1
Views
1K
Deleted member 120897
D
10 o’clock / 45 degrees would be better than...
Replies
3
Views
692
  • Question
So have started fitting all the bits together...
Replies
15
Views
2K
Back
Top