Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss baxi 105 heating problems in the Plumbing Jobs | The Job-board area at Plumbers Forums

Status
Not open for further replies.

plumbbobshan

Gas Engineer
Messages
77
hi lads ,
baxi 105 heating problems, flow pipe mad hot, return pipe cool, boiler up to temp in about 2 mins, hot water fine, pump running fine, plate heat ex acid dipped 3 weeks ago, top pin on diverter valve in the up position all the time.
was thinking diverter valve jammed up ??? and needs either replace or repair.
any help much appreciated.
bob
 
try pushing pin down defo sounds like diverter problem,if able get refurb kit or better still get some one in
 
Status
Not open for further replies.

Similar plumbing topics

Chris, just to update, thanks for all your...
Replies
3
Views
678
  • Question
Problem found, it was a blockage... mostly in...
Replies
11
Views
1K
Heating will run until hot gets up to...
Replies
1
Views
897
Back
Top