Leo21

Esteemed
Plumber
Gas Engineer
Subscribed
Messages
9,306
As above 105e flashing on 30 and 50. Never seen this before, anybody else seen it? I'm sure it's the pcb, I've ordered a new one. Thought I'd seen everything on these.
 
30 is flame failure 50 is fan,so either fan relay,aps ,ignition system or fan,also do basic electrical checks,mains in, RP etc
 
Both lights flashing at the same time Mark. The fan doesn't start. So can't be aps or flame failure if it's not getting that far into the cycle.
 
Both lights flashing at the same time Mark. The fan doesn't start. So can't be aps or flame failure if it's not getting that far into the cycle.

agree,remove pcb cover and check for water,have you done basic elec checks?
 
Pcb was dry, haven't checked polarity. They normally cycle when wrong don't they? Anyway, thanks for the help Mark.
 
Pcb was dry, haven't checked polarity. They normally cycle when wrong don't they? Anyway, thanks for the help Mark.

no,normally when polarity is revered or voltage to high they see a flame failure fault or flash up weird lights,probably is pcb but woth checking the basics or it will fry the new one
 
Status
Not open for further replies.

Similar plumbing topics

No you couldn’t need to be gas safe
Replies
9
Views
792
You need a new service engineer not a new...
Replies
3
Views
980
  • Locked
you very rarely need the condy trap you just...
Replies
17
Views
275
The 830 and 630 are the same boiler, just the...
Replies
7
Views
252
All sorted now and running better than ever...
Replies
3
Views
1K
Back
Top