I am sure there was a post about this before but here we go....

Callout to 105e in a loft no light etc, boiler on lock out no gas fault 30 deg led flashing etc, gas at inlet so thought valve had stuck as house had been empty 8 weeks, banged no joy!

240v at pins 2 and 4 of pcb so, i get a new gas valve as the multi plug on the valve aint easy to get test probes in and in a black loft working via head torch, anyhow gas valve swapped, same fault so test continuity of wires from pcb plug to plug on gas valve, wire is approx 18" long, neutral and earth fine, but nothing on live, this is when i notice the plug on the gas valve has some sort of recitifer built in, its sealed so no chance of a look.

Ordered a new lead with plugs , that also feeds the spark gen.

Anyone else been caught with this? is the gas valve DC? forgot to look after i left job, or is there a diode in the multi plug that has failed and the valve is AC? NOT THE MODIREG i know this is DC and is fed via 2 other black wires!
 
yes the valve is dc to stop it buzzing apparently, was chatting to a heat team engineer in hrpc about similar prob though i had fettled it by then but was curious, there is a little pcb in the gas valve connecting plug
 
yes the valve is dc to stop it buzzing apparently, was chatting to a heat team engineer in hrpc about similar prob though i had fettled it by then but was curious, there is a little pcb in the gas valve connecting plug

so did the new lead with plug sort it tom? as that is all i can think it is......gonna cut the old one open
 
it was actually the valve though i had a new cable with me in case
 
it was actually the valve though i had a new cable with me in case

lol cable is cheaper, but not when you have fired a gas valve in, that will teach me...thing is i read MI's after it does not even mentioned cable....gas valve then pcb typical
 
i posted one on here similar changed the lead and gas valve andvoltages were ok and the 12v to modulator so flame should have been full power but didnt never got to the bottom of it.baxi told me it was impossible to get true reading from that that magic ac/dc lead
 
Right update....fitted lead problem solved, had more time so put old valve back in, lockout, put new gas valve back in job sorted, set up a high and low sorted......theory gas valve took out PCB in lead eventully....

cut old plug open and indeed PCB in there looks like a basic capacitor smoothing circuit for noise suppression, components all black and smelly, got a pic will upload later!

one to remember boys!

yest ant voltages at plug mean bobbins, you cannot even test continuity of wires to pin, tried weather you buzz the live or neutral at PCB plug, you get continuity on the outer top pin, obviously the PCB screws the readings!

lead part no is 248218 for future ref
 
Picture of said plug as promised....toast
Baxi gas valve plug.jpg
 
Status
Not open for further replies.

Similar plumbing topics

Is it very fine particles almost like pencil...
Replies
13
Views
189
Also, they could even supply their own tube...
Replies
19
Views
2K
I have connected the secondary pump to a wifi...
Replies
9
Views
2K
H
Hi there, thanks for your time to look at this...
Replies
0
Views
913
HRP123
H
Your gas rate is your big one to check. Well...
Replies
9
Views
215
Back
Top