Ladies and Gents, advice needed please
In the last couple of days my Baxi 105e has started being slow to heat the radiators and will only give me hot water at a trickle, if I turn the water on above half way it runs cold. We have recently had gas mains work done in our area which also required me to have a new governor on the meter, I thought it might be a gas pressure problem so I called the gas man back who said I am getting 22millibars and that can't be the problem.
I have checked the diaphragms in the diverter and the pressure diff and they are fine, checked and cleaned the diverter and phex and they are ok also.
There are no fault lights, burner fires up with no problems and fires all the time the DHW is running, diverter is not bypassing down the ch
Starting to suspect the primary heat exchanger and/or gas pressure issue, however I am not gas registered so I will not touch this parts, my question is are there any other parts that may be responsible, temp sensors, switches etc that would give these symptoms and that I can change before calling an engineer.
Thanks in advance for any advice
In the last couple of days my Baxi 105e has started being slow to heat the radiators and will only give me hot water at a trickle, if I turn the water on above half way it runs cold. We have recently had gas mains work done in our area which also required me to have a new governor on the meter, I thought it might be a gas pressure problem so I called the gas man back who said I am getting 22millibars and that can't be the problem.
I have checked the diaphragms in the diverter and the pressure diff and they are fine, checked and cleaned the diverter and phex and they are ok also.
There are no fault lights, burner fires up with no problems and fires all the time the DHW is running, diverter is not bypassing down the ch
Starting to suspect the primary heat exchanger and/or gas pressure issue, however I am not gas registered so I will not touch this parts, my question is are there any other parts that may be responsible, temp sensors, switches etc that would give these symptoms and that I can change before calling an engineer.
Thanks in advance for any advice