Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss baxi 105e in the Plumbing Jobs | The Job-board area at Plumbers Forums

Status
Not open for further replies.
Could be loads of things and your question is far too vague.
Is there power to the boiler and are the controls calling for heat?
If your not sure, call a GSR.
 
Hi pl1, try the following.

Does it work when demand for heating?

Are the two micro switches being operated when tap opened. Each has it's own diaphragm.

If these ok then Is the fan free to move? With no demand try and give it a spin by hand.

If its seized then needs replacing.

If fan free to move then check with multimeter for 240v across fan coil.

If 240v present, fan problem. If not then something prior to the fan on ignition train or main board.
 
hi guys yes power to boiler ch working fine just no fire up on hw thought maybe dhw sensor fault
 
As CH working ok then check DHW microswitch being operated, possible split diaphragm.
 
Hi pl1, try the following.

Does it work when demand for heating?

Are the two micro switches being operated when tap opened. Each has it's own diaphragm.

If these ok then Is the fan free to move? With no demand try and give it a spin by hand.

If its seized then needs replacing.

If fan free to move then check with multimeter for 240v across fan coil.

If 240v present, fan problem. If not then something prior to the fan on ignition train or main board.

very regimental are you ex army.left ,right, left ,right.
 
Status
Not open for further replies.

Similar plumbing topics

Chris, just to update, thanks for all your...
Replies
3
Views
678
faulty diaphram with the sound of it.
Replies
1
Views
721
  • Question
Do you have to send the old one back ?
Replies
5
Views
1K
Upto you the duo has a flow rate of 11 as the...
Replies
4
Views
2K
How did you get the valve sorted in the end?
Replies
1
Views
463
Back
Top