Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Baxi 80 combi boiler in the Boilers area at Plumbers Forums

Status
Not open for further replies.
R

rmbp

Hello there, I've got a baxi 80 combi thats losing pressure, all pipework is exposed and there no leaks. The rad's are ok, If I set pressure to 2bar It drops down to 0.5 bar in about tens minutes. The heating works fine until the pressure drops and the hot water operates no problem. But can't figure out why the pressure is dropping, Any suggestions are welcome.
This problem seems to occur quicker when the heating is turned off.
 
Last edited by a moderator:
have you checked the pressure relif valve outside ? is it dripping/ running?could besome muck in the valve stopping it from shutting off properly.
 
The other possibility is the main heat exchanger is leaking into the sump and draining away through the condensate drain.

Does this just happen when it is working or all the time?

If it is all the time you can narrow down the cause by re-pressurising the system and shutting the boiler isolating valves. If the pressure drops at the boiler the fault is within the boiler. If it stays steady and then drops when the valves are re-opened it is in the pipework. Obviously don't run the boiler while you are checking this.

Mike
 
Hello there, I've got a baxi 80 combi thats losing pressure, all pipework is exposed and there no leaks. The rad's are ok, If I set pressure to 2bar It drops down to 0.5 bar in about tens minutes. The heating works fine until the pressure drops and the hot water operates no problem. But can't figure out why the pressure is dropping, Any suggestions are welcome.
This problem seems to occur quicker when the heating is turned off.
Just replaced the prv everything spot on, Thanks for advice.
 
Status
Not open for further replies.

Similar plumbing topics

What the easiest way to find why my boiler is...
Replies
0
Views
524
M
Isolate and drain boiler. Pump up expansion...
Replies
1
Views
728
It’s an automatic air vent - you can close it off.
Replies
1
Views
1K
Deleted member 120897
D
Thanks for the reply, I’ll try your...
Replies
4
Views
863
You need a new service engineer not a new...
Replies
3
Views
927
Back
Top