Baxi duo-tec 2 combi 24 ga no hot water no fault code | Bathroom Advice | Plumbers Forums

Welcome to the forum. Although you can post in any forum, the USA forum is here in case of local regs or laws

Discuss Baxi duo-tec 2 combi 24 ga no hot water no fault code in the Bathroom Advice area at Plumbers Forums

J

johnnyboyoy

Hi there, went to look at the above last night. Heating fine. Hot water, led flashes on Hall effect sensor. Boiler display never shows demand for hot water. Checked between red and blue from HES on pcb for approx 5vdc, flicked between 1.25v to 2.5v. Flow chart says that if I have approx 5v change HES and if not change PCB. When reading the introduction to DHW in this boilers manual and in the flow chart for the main combi elite (which I'd thought would work in a similar way) it seems to suggest that the diverter has to move in order to start firing sequence. Guess I need to call baxi tomorrow but wondering if anyone has any experience of this? Thanks
 
unless your gas safe you shouldn't touch/ take the cover off
 