Hello All,
I am currently having an issue with my Baxi Duo Tec 40 HE A not maintaining a constant temperature for the domestic hot water.
With a thermometer under a tap & the domestic hot water thermostat set to 43 °C I get a fluctuating temperature from 51 °C to 38 °C which is clearly not acceptable as it goes from warm to scalding.
I have uploaded a video of the boiler to YouTube below showing what happens when you create a hot water demand by turning a tap on.
As you can see the burner does not stay on but cycles on & off because it seems to me the primary water in the boiler is getting to hot so the PCB is turning the burner off?
What I have found is that if I turn two taps on at the same time the problem is fixed!
The boiler modulates the temperature correctly & I get around 43°C at the tap give or take 2 degrees.
I have boiler cover plan so I contacted them & they sent an engineer out & so far they have changed the following components:
1. Diverted Valve
2. Domestic Hot Water Thermistor
3. Plate Heat Exchanger
4. PCB
All genuine Baxi parts & I still have the same problem so clearly non of these components were faulty.
The warranty company is now saying that because they have spent all this money on these components & it has not fixed the problem the I need a new boiler!
At this point I have lost all trust in them & the engineers capability to diagnose the problem.
I am currently trying to get recommendations for a gas engineer in my area but am struggling to do so & am wanting others opinions on what could be causing this.
This has taken place over a four month period due to COVID.
Here is the video of the boiler with one tap running creating a hot water demand:
View: https://www.youtube.com/watch?v=f_6SGMUkAU0&feature=emb_logo
As you can see the burner switches on & off causing the temperature to fluctuate.
Here is a video of the boiler with TWO taps running creating a hot water demand:
View: https://www.youtube.com/watch?v=DyzUVARBvdI&feature=emb_logo
& here the burner stay lit constantly fixing the problem!
Any ideas what could be causing this & why it is fixed by turning two taps on?
Many thanks
Adam
[automerge]1592268441[/automerge]
Can an admin or moderator please move this thread to the gas engineers forum please?
Sorry I posted it in the wrong section.
Thank you
I am currently having an issue with my Baxi Duo Tec 40 HE A not maintaining a constant temperature for the domestic hot water.
With a thermometer under a tap & the domestic hot water thermostat set to 43 °C I get a fluctuating temperature from 51 °C to 38 °C which is clearly not acceptable as it goes from warm to scalding.
I have uploaded a video of the boiler to YouTube below showing what happens when you create a hot water demand by turning a tap on.
As you can see the burner does not stay on but cycles on & off because it seems to me the primary water in the boiler is getting to hot so the PCB is turning the burner off?
What I have found is that if I turn two taps on at the same time the problem is fixed!
The boiler modulates the temperature correctly & I get around 43°C at the tap give or take 2 degrees.
I have boiler cover plan so I contacted them & they sent an engineer out & so far they have changed the following components:
1. Diverted Valve
2. Domestic Hot Water Thermistor
3. Plate Heat Exchanger
4. PCB
All genuine Baxi parts & I still have the same problem so clearly non of these components were faulty.
The warranty company is now saying that because they have spent all this money on these components & it has not fixed the problem the I need a new boiler!
At this point I have lost all trust in them & the engineers capability to diagnose the problem.
I am currently trying to get recommendations for a gas engineer in my area but am struggling to do so & am wanting others opinions on what could be causing this.
This has taken place over a four month period due to COVID.
Here is the video of the boiler with one tap running creating a hot water demand:
View: https://www.youtube.com/watch?v=f_6SGMUkAU0&feature=emb_logo
As you can see the burner switches on & off causing the temperature to fluctuate.
Here is a video of the boiler with TWO taps running creating a hot water demand:
View: https://www.youtube.com/watch?v=DyzUVARBvdI&feature=emb_logo
& here the burner stay lit constantly fixing the problem!
Any ideas what could be causing this & why it is fixed by turning two taps on?
Many thanks
Adam
[automerge]1592268441[/automerge]
Can an admin or moderator please move this thread to the gas engineers forum please?
Sorry I posted it in the wrong section.
Thank you