I posted earlier about our hot water cycling on and off but now its got worse
When a hot water tap is opened, water starts to flow, the boiler fires up and the boiler temp display goes up slowly to around 60 degrees, all as usual, and the water gets warm. Then, the boiler temp starts to rise very fast, there's a rattling noise from the boiler and at 95 degrees the burner cuts out. While this is happening the water goes cool again. This cycles for as long as the tap is on.
I've checked the central heating works normally, and the system pressure is normal but a fault code of E125 came up earlier, any ideas please ?
When a hot water tap is opened, water starts to flow, the boiler fires up and the boiler temp display goes up slowly to around 60 degrees, all as usual, and the water gets warm. Then, the boiler temp starts to rise very fast, there's a rattling noise from the boiler and at 95 degrees the burner cuts out. While this is happening the water goes cool again. This cycles for as long as the tap is on.